I have a bad start cap on an air compressor.
The old cap has a nice shiny spot where the size was. All I can see is the voltage.
Grainger found what might be the right size, and I have one coming.

The question is what if it is not the right size? What can I expect if it is too small or too large?
1 - 20 of 30 Posts
Too small it may not start or over amp and trip off, too large can be okay. Either way check the amp draw starting and running.
  • Like
Reactions: 4
Too small it may not start or over amp and trip off, too large can be okay. Either way check the amp draw starting and running.
Good to see you back!
Thanks. We have a 4micro farad coming.
  • Like
Reactions: 3
Good to see you back!
Thanks. We have a 4micro farad coming.
4 micro farad is more inline with a run capacitor than a start capacitor. For example, a 1/2Hp submersible pump has a start capacitor of around 110 micro farads.
  • Like
Reactions: 2
Does it have 1 or 2 caps?

As noted, if it's the start cap and it's too small, it will have less starting torque and it'll growl at you.

There's no way to calculate the cap rating, every manufacturer is different.
Did you find the manual for the compressor/motor?
Here is a pretty good article on caps.
About 1/3 of the way down you’ll see the part you’re looking for.
MechanicalDVR is right, over sizing isn’t to bad.

  • Like
Reactions: 4
Good to see you back!
Thanks. We have a 4micro farad coming.
Thanks, nice to be back.

What hp compressor? Sounds small.
  • Like
Reactions: 1
I have a bad start cap on an air compressor.
The old cap has a nice shiny spot where the size was. All I can see is the voltage.
Grainger found what might be the right size, and I have one coming.

The question is what if it is not the right size? What can I expect if it is too small or too large?
if the cap is metal cased and around 4mfd
it is not a start cap

it is a run cap ...... exact size matters a great deal

as mentioned performance will decrease if the size is wrong
and the size of the case is not a good indicator of mfd size

start caps are nonmetal cased and in the hundreds of mfd
larger mfd is better, higher voltage is better

run caps are always metal cased and less than a hundred mfd
larger or smaller mfd is bad, higher voltage is better

a higher voltage rating on a cap simply means the insulation is better, it will last longer
always get higher voltage if possible

this is where i buy caps
See less See more
  • Like
  • Helpful
Reactions: 3
Thanks for the responses. The motor is 5 hp, single phase.
The motor has 3 caps. 1 is bad, and the motor hums and trips the breaker. The other two are good and they are round plastic, while the bad one is oblong and metal.

The cap didn’t come in anyway, so it will be next week when I get back and see what happens.
Something else may be wrong........

That motor is cap start-cap-run. The metal cap is always in series with the start winding, hence the 'cap-run'. The other 2 caps are connected in parallel (in order to get a higher µF rating. They are also in parallel with the run cap during starting then the centrifugal switch disconnects them.

If the run cap failed shorted (fairly rare but it does happen) then the motor will not turn but will draw tons of current. If it failed open (they usually do) then the motor will start as usual but it'll run at reduced HP.

If the run cap failed open and the motor won't start and draws a ton of current, most likely the centrifugal switch is stuck open and the start caps are not in the circuit.
  • Like
Reactions: 2
Something else may be wrong........

That motor is cap start-cap-run. The metal cap is always in series with the start winding, hence the 'cap-run'. The other 2 caps are connected in parallel (in order to get a higher µF rating. They are also in parallel with the run cap during starting then the centrifugal switch disconnects them.

If the run cap failed shorted (fairly rare but it does happen) then the motor will not turn but will draw tons of current. If it failed open (they usually do) then the motor will start as usual but it'll run at reduced HP.

If the run cap failed open and the motor won't start and draws a ton of current, most likely the centrifugal switch is stuck open and the start caps are not in the circuit.
A little confusing here. A starting cap is in series with the starting coil.

Starting caps are quite often but not always the biggest ones and my experiences is often in parallel for motors that size. They are always electrolytic types which are notorious for short life (8-10years). As stated they are often 100-500 microfarads. Run caps are usually under 100. There is no formula for caps. In the shop they vary the run cap for lowest no load amps (ideally zero). They vary the start cap for max torque at stall or to give about a 35 degree phase angle advance. So if you have a scope with an amp clamp and know what you are doing it’s easy to pick one. Centrifugal switches are common but not the only way.Potential relays or just timers are the other two. The start coil only energized a second or two to give the motor a kick in the right direction and help boost starting torque (which is crap on single phase). After that it becomes a drag (load) and sucks high amps so must be disconnected before the start cap explodes or the start coil burns up.

Single phase motors are actually harder than three phase.
See less See more
Ok. Thanks for the heads up. Looking back, I think it is the run cap and not the start cap.
So the cap came in today. It was a 5uf, at 440 volts. I installed it and turned the unit back on. It still had the hum as before, but it started this time. , and the hum went away. I didn't run it but a few seconds, since it is quitting time, and I didn't want it running overnight with no one here. I think it may be 2 small.
Since I don't have a scope, and if it was you, what size next would you try?
1/2 mfd larger
also
1/2 mfd smaller

the best thing to do is find someone who has the exact motor you have and find out what size cap theirs is

the next best thing is to buy a cap meter, measure the old cap, whatever it is the new one should be larger
start creeping up in size till it runs the way it used to
Nameplate photo?
Liquid Tin Fluid Drink Paint

Grab one of these and try different combinations until you hit the right size. I have one on the truck for emergency situations that can arise until I can get the proper size for a motor.
See less See more
  • Like
  • Helpful
Reactions: 2
1/2 mfd larger
also
1/2 mfd smaller

the best thing to do is find someone who has the exact motor you have and find out what size cap theirs is

the next best thing is to buy a cap meter, measure the old cap, whatever it is the new one should be larger
start creeping up in size till it runs the way it used to
I do have a cap meter and it reads open.
  • Sad
Reactions: 1

Attachments

See less See more
4
Check the start caps. It sounds like one or both may be going bad. If it has problems starting but runs ok, it's not the run cap; more likely it's the start caps. In your case, the start caps operate in parallel.
  • Like
Reactions: 1
Here is the manual. Looks like you need to reference the motor model in it for the replacement cap.