Registered
Joined
·
8,054 Posts
One or the other. VFD cable inside a steel conduit is pointless IMO. I've never even used the VFD cable. All the motor runs I do need physical protection that VFD cable can't offer so it's going to be in grc or EMT anyway.
 

·
Electron Flow Consultant
Joined
·
3,309 Posts
Discussion Starter · #3 ·
One or the other. VFD cable inside a steel conduit is pointless IMO. I've never even used the VFD cable. All the motor runs I do need physical protection that VFD cable can't offer so it's going to be in grc or EMT anyway.
It's not armored or installed in tray. It will be in conduit, steel or aluminum?
 

·
Registered
Joined
·
8,054 Posts
sparky970 said:
It's not armored or installed in tray. It will be in conduit, steel or aluminum?
Is the cable speced or do you need auxiliary contacts ran with the motor feeders? If not I'd just use THHN in steel conduit. But if I HAD to use the cable and I needed to protect it I'd put it in steel conduit simply because I don't keep aluminum around. It's a bit redundant but it won't hurt anything
 

·
Registered
Joined
·
5,652 Posts
It's not armored or installed in tray. It will be in conduit, steel or aluminum?
Steel, you need the magnetic shielding it provides if you do not use shielded VFD cable, aluminum is non-magnetic so it might as well be PVC. Ground the conduit at BOTH ends.

But if you use steel conduit, the VFD cable is a little redundant.

Most VFD mfrs will now tell you NOT to use THHN by the way, the PVC insulation used to make it can have voids (bubbles) in it that compromise the insulation in the presence of what are called "standing waves" of higher voltage pulses that can be created by cable capacitance between the conductors as a result of the high speed DC switching that makes up the PWM output of a VFD. The recommended wire type, if NOT using VFD cable, is XLPE (most VFD cable uses XLPE too). The insulation thickness is more uniform and there are no voids in the plastic.

575V, 125hp motor. He specified inverter rated cable
The other advantage of VFD cable then is that it is typically rated for 1000V. On a 575V drive, your DC bus voltage, and thereby the voltage of the pulses going to the motor, is 810V. 600V cable is generally considered OK for 480V drives, but you get a little more dicey at 575V if there are any standing waves going on.
 

·
Registered
Joined
·
8,054 Posts
JRaef said:
Steel, you need the magnetic shielding it provides if you do not use shielded VFD cable, aluminum is non-magnetic so it might as well be PVC. Ground the conduit at BOTH ends. But if you use steel conduit, the VFD cable is a little redundant. Most VFD mfrs will now tell you NOT to use THHN by the way, the PVC insulation used to make it can have voids (bubbles) in it that compromise the insulation in the presence of what are called "standing waves" of higher voltage pulses that can be created by cable capacitance between the conductors as a result of the high speed DC switching that makes up the PWM output of a VFD. The recommended wire type, if NOT using VFD cable, is XLPE (most VFD cable uses XLPE too). The insulation thickness is more uniform and there are no voids in the plastic.
Good to know about the xlpe. So what's your opinion on the millions of installs done with conduit and THHN? Still good?
 

·
Registered
Joined
·
5,652 Posts
Good to know about the xlpe. So what's your opinion on the millions of installs done with conduit and THHN? Still good?
No point in changing it if it hasn't failed yet. But if it does, change it with XLPE. The entire issue came up BECAUSE of a higher number of cable failures being reported to major cable mfrs. It's not a high number, but it is significantly higher than it was before (or without) VFDs.
 

·
Electron Flow Consultant
Joined
·
3,309 Posts
Discussion Starter · #9 ·
Steel, you need the magnetic shielding it provides if you do not use shielded VFD cable, aluminum is non-magnetic so it might as well be PVC. Ground the conduit at BOTH ends.

But if you use steel conduit, the VFD cable is a little redundant.

Most VFD mfrs will now tell you NOT to use THHN by the way, the PVC insulation used to make it can have voids (bubbles) in it that compromise the insulation in the presence of what are called "standing waves" of higher voltage pulses that can be created by cable capacitance between the conductors as a result of the high speed DC switching that makes up the PWM output of a VFD. The recommended wire type, if NOT using VFD cable, is XLPE (most VFD cable uses XLPE too). The insulation thickness is more uniform and there are no voids in the plastic.



The other advantage of VFD cable then is that it is typically rated for 1000V. On a 575V drive, your DC bus voltage, and thereby the voltage of the pulses going to the motor, is 810V. 600V cable is generally considered OK for 480V drives, but you get a little more dicey at 575V if there are any standing waves going on.

I was hoping you would give some input. Before there wasn't much "vfd" cable, it was always in steel conduit, never aluminum. I've been looking but can't find anything that backs up, the type of conduit.
 

·
Registered
Joined
·
5,652 Posts
I was hoping you would give some input. Before there wasn't much "vfd" cable, it was always in steel conduit, never aluminum. I've been looking but can't find anything that backs up, the type of conduit.
Regardless of what brand of drive you use, this is the best document I've ever found on VFD installation. It originated with the old Reliance drives group when AB bought them, but has been continuously updated over the years. When I worked for ABB and again for Siemens later, I used to tear the covers off of this and give it to my customers...

The Bible of VFD installation...

Pay particular attention to Chapter 5
 

·
Electron Flow Consultant
Joined
·
3,309 Posts
Discussion Starter · #11 ·
Regardless of what brand of drive you use, this is the best document I've ever found on VFD installation. It originated with the old Reliance drives group when AB bought them, but has been continuously updated over the years. When I worked for ABB and again for Siemens later, I used to tear the covers off of this and give it to my customers...

The Bible of VFD installation...

Pay particular attention to Chapter 5
Thanks, I had just downloaded that pdf but hadn't read it yet.
 

·
Electron Flow Consultant
Joined
·
3,309 Posts
Discussion Starter · #14 ·
what exactly is xlpe? It is not an insulation type that is permitted for single conductors installed under the rules of the nec. Does it go by another name in table 310.104?
RHH/RHW-2 and XHHW are showing up as alternatives to THHN in acidic environments for two reasons: They both use cross-linked polyethylene (XLPE) insulation rather than PVC. Second, they both offer more insulation thickness than THHN. XHHW offers a little more thickness, RHH/RHW offers quite a bit more. In general, in the demanding waste-water treatment environment, the thicker the insulation, the better off you are.

Here’s an example: A single-conductor 350 kcmil THHN cable uses 60 mils of PVC. An XHHW conductor delivers 65 mils of XLPE. RHH-RHW gives you 95 mils of XLPE. The table below summarizes the constructions.
 

·
Registered
Joined
·
13 Posts
Drop a High powered magnet down an Aluminum or copper. The Magnet will slowly hover down the center. You tube "aluminum tube magnet" and watch, Eddy currents slow it down, It's neat.
Based on that, I don't think it matters if you use Steel or AL Conduit.
Doesn't VFD and many other cables use Aluminum coated mylar or plastic and Copper braid.
 

·
Registered
Joined
·
6,205 Posts
Regardless of what brand of drive you use, this is the best document I've ever found on VFD installation. It originated with the old Reliance drives group when AB bought them, but has been continuously updated over the years. When I worked for ABB and again for Siemens later, I used to tear the covers off of this and give it to my customers...

The Bible of VFD installation...

Pay particular attention to Chapter 5
That's awesome info man. I don't get to play with VFDs and whatnot anywhere near as much as I would like, but that is something I never would have thought of. Thanks! :thumbup:
 

·
Banned
Joined
·
16,967 Posts
Most VFD mfrs will now tell you NOT to use THHN by the way, the PVC insulation used to make it can have voids (bubbles) in it that compromise the insulation in the presence of what are called "standing waves" of higher voltage pulses that can be created by cable capacitance between the conductors as a result of the high speed DC switching that makes up the PWM output of a VFD. The recommended wire type, if NOT using VFD cable, is XLPE (most VFD cable uses XLPE too). The insulation thickness is more uniform and there are no voids in the plastic.
To my knowledge, FANUC has no such requirement. We regularly use THHN/THWN for VFD circuits, and the ready made VFD cable from FANUC for larger motors is nothing more than rubber cord.
 

·
Data Tech/Apprentice.
Joined
·
9,013 Posts
Drop a High powered magnet down an Aluminum or copper. The Magnet will slowly hover down the center. You tube "aluminum tube magnet" and watch, Eddy currents slow it down, It's neat.
Based on that, I don't think it matters if you use Steel or AL Conduit.
Doesn't VFD and many other cables use Aluminum coated mylar or plastic and Copper braid.
Aha! Our instructor did that to us and we couldnt figure it out.
 

·
Registered
Joined
·
747 Posts
here we use 1kv teck cable for 600v vfd and never had problem, teck cable have xlpe wiring inside
Tec is the best.:thumbsup:
 