What do you do when the cable your using isn't on table D3? Like 250, or 300?

trying to figure out voltage drop for an underground 400amp parallel runs.
87m approx
I know there is a formula for this somewhere in my books
 

· Registered
Joined
·
12 Posts
Discussion Starter · #2 ·
I think I found my answer. If someone would be kind to verify this
Parallel runs of 250kcmil for a 400a service approx 87m (285')


L=RxCMA
-----------
K

(285x17) / 250000 = R

R = .01938ohms per conductor
.01938 x 2 = .03876ohms total
200a x .03876 = V
V = 7.752
(7.752x100) / 240 = 3.23% voltage drop
Should be okay with 250kcmil eh? :wacko:
 

· Banned
Joined
·
7,205 Posts
See note #6

(6) The distances and currents listed in Table D3 follow a pattern. When the current, for any conductor size, is increased by a factor of 10, the corresponding distance decreases by a factor of 10. This relationship can be used when no value is shown in the table. In that case, look at a current 10 times larger. The distance to the centre of distribution is then 10 times larger than the listed value.
 