OP is in Canada...I'd use a 30 and #12. Yes, it's code compliant. Since you're an apprentice, you should have access to a codebook so you can look at articles 430 and 240 to see that using #12 with a 30 amp breaker is legal with a motor.
That motor doesn't have any overload protection. Article 430 states that O/L is required so you'll need to provide it separately. A single phase motor starting switch with O/L built in would be the easiest. I usually use the Square D 2510 class.
Please take a few minutes to fill out your profile. Here's a link to help you do this quickly.Hey guys I’m a newbie in the trade first year. So to wire this table saw to work properly(115 volts) I would need a 20 amp plug and 20 amp breaker right? With 12/2 wire? View attachment 154062
Canadianized it for you!I'd use a 30 and #12. Yes, it's code compliant. Since you're an apprentice, you should have access to a codebook so you can look at section 28 to see that using #12 with a 30 amp breaker is legal with a motor.
That motor doesn't have any overload protection. section 28 states that O/L is required so you'll need to provide it separately. A single phase motor starting switch with O/L built in would be the easiest. I usually use the Square D 2510 class.
So no over load protection is required in Canada? our SH’s carry 40/2 breakers, they are also on eBay.Canadianized it for you!
Ideally I would wire it with a 20A breaker and #14 wire at 230V. At 115V, a #12 will work for wire and the 30A breaker is a good start. By code you could put it on a 40A breaker if you needed too, but good luck finding one.
Being a grunt it’s been awhile since I had my head into code but aren’t we supposed to multiply the fla (18A if it’s going to be 120v) by 125% and go with the minimum ga conductor/ocd above that? In that case it’d be #10&30A ocd?Canadianized it for you!
Ideally I would wire it with a 20A breaker and #14 wire at 230V. At 115V, a #12 will work for wire and the 30A breaker is a good start. By code you could put it on a 40A breaker if you needed too, but good luck finding one.
I would run ten Guage. But more likely I'd put a 240 receptacle in, that's a big shop saw so it's not getting moved around all over the place.Being a grunt it’s been awhile since I had my head into code but aren’t we supposed to multiply the fla (18A if it’s going to be 120v) by 125% and go with the minimum ga conductor/ocd above that? In that case it’d be #10&30A ocd?
Thanks!Canadianized it for you!
Ideally I would wire it with a 20A breaker and #14 wire at 230V. At 115V, a #12 will work for wire and the 30A breaker is a good start. By code you could put it on a 40A breaker if you needed too, but good luck finding one.
A single phase dual voltage motor with built in O/Ls will have 7 (or more) leads. This one has 6 so no built in O/L.Take your motor ampacity and multiply by 125% and that will tell you what ampacity you need for your wire. Assuming the motor has overload protection built in then you can use an overcurrent protective device at 250% for the nec. I bet it is similar for the CEC, if not then canada is wrong...LOL
The wiring diagram looked a little off, now I know why.A single phase dual voltage motor with built in O/Ls will have 7 (or more) leads. This one has 6 so no built in O/L.
Get used to questions that is how you learn, the more information you give up front is better then we don't have to guess.Hey guys I’m a newbie in the trade first year. So to wire this table saw to work properly(115 volts) I would need a 20 amp plug and 20 amp breaker right? With 12/2 wire?
First and foremost thanks for the reply I need all the help i can get . Sorry for the confusion from my initial post.Couple of questions
1. Is this for you? If so just run it on what you have.
2. Does it have a starter or switch installed?
2. Terminology. You said you would need a "I would need a 20 amp plug and 20 amp breaker right? With 12/2 wire"
This is why you got a variety of answers, You talk Plug when I guess you meant receptacle. If it was Plug then it would be 12/3 cord not 12/2 wire.
Get used to questions that is how you learn, the more information you give up front is better then we don't have to guess.
Good job asking the questions here and not just guessing.
Cowboy
What brand of panel?First and foremost thanks for the reply I need all the help i can get . Sorry for the confusion from my initial post.
1. It is for my buddy in a garage. it just keeps tripping the breaker with what it currently has. A 15a cord end as shown in my attached pic. The cord wire is 14awg.
2. It has a switch installed.
3. Yeah i meant what kind of receptacle do i need to install for this saw. I really just don’t know what this needs to run properly. What kind of cord end? What size of wire, what kind of receptacle. Oh man. so many questions.