Discussion Starter · #1 ·
I have 10, 4 inch PVC pipes entering the back of a 3000 amp switchgear.

I am told I do not need to punch holes and terminate in adapters with locknuts and bushings. I can just cut out the back of the gear to fit the pipes and install end bells and call it good.

This is not normally what I would do, but I can not find where it would be a violation. I briefly looked in 300.

Do I need to use male adapters dressed up?
 

Attachments

· Mad Skills
Joined
·
5,798 Posts
I have 10, 4 inch PVC pipes entering the back of a 3000 amp switchgear.

I am told I do not need to punch holes and terminate in adapters with locknuts and bushings. I can just cut out the back of the gear to fit the pipes and install end bells and call it good.
What is punching out 10 - 4" holes going to accomplish?
Will connecting the pipes to them bond anything?
Prevent movement?
Protect the conductors from damage?
etc?

What is the actual purpose?
 

· Salty Member
Joined
·
31,030 Posts
And in case any of you are wondering where all the buss bars are....check with some Scrapyard's.

Thief's.
This gear was stripped overnight a couple months ago.
Looks like a housekeeping pad would have been a good idea.

If I was the customer I would have a real problem with the bottom of my brand new gear sitting in water.
 