I m having a vfd of altivar 71 60 HP I want to test it on single phase .... does any one have procedure for testing it .... n do somebody have knowledge of how to test vfd by connecting lamp on load side .... please give me solution
 

· animal lover /rat bastard
Joined
·
13,504 Posts
wire something up so you got around 50kw of 3 phase and you're good to go (rotary phase converter, motor generator, whatever). if you can't figure out how to test the outputs why are you even messing with it ? what part of india are you working at ?
 

· Registered
Joined
·
3 Posts
Discussion Starter · #3 ·
wire something up so you got around 50kw of 3 phase and you're good to go (rotary phase converter, motor generator, whatever). if you can't figure out how to test the outputs why are you even messing with it ? what part of india are you working at ?
Thank u very much for the reply ..... btw dear .... m not messing with up .... but in the manual of altivar it has been written tat vfd can b test without output or low load ....so I just wanted to know the method that's it
 

· Registered
Joined
·
5,767 Posts
sonu1232 said:
Thank u very much for the reply ..... btw dear .... m not messing with up .... but in the manual of altivar it has been written tat vfd can b test without output or low load ....so I just wanted to know the method that's it
If you will not have a 3 phase MOTOR load, you cannot test all functionality of the drive. A PWM drive output is not really AC, but it ACTS like AC in an inductive machine like a motor. Without the motor, you can look at the output with a scope to see the DC pulses, but other than that all you can "test" is that the electronics are working. You can hook up lamps in a 3 phase delta to the load terminals to see if the transistors are firing, but that will not really indicate much more than basic functionality. You would need to ensure that you have enough lamps in series on each phase to prevent them from burning out immediately from high voltage, but not knowing your voltage, you will have to determine that yourself.

If that Is all you want to do, then you can power it from single phase of the rated voltage of the drive, but you will need to know how to turn off the Phase Loss trip protection in the drive.
 

· Registered
Joined
·
3 Posts
Discussion Starter · #5 · (Edited)
Thank u very much .....that option I can make it off from fault management menu..... can u pls gv me a detail of this lamp connection pls because I was looking for this way of testing only .... pls gv me the detail

Can u pls also tell me how to test IGBT
 