I have to wire a transformer tomorrow for a practical evaluation in school.
It is a small dry type (25kva I think) that is being fed from a 480 panel and feeds a 120/208 panel. I would appreciate if you guys could tell me if I am missing anything as far as procedure. The transformer will have FMC going to it on both sides.
Primary side:
determine feeder ampacity according to 215.2(B)1 (kva/480).
determine wire size according to 310.15(b)16
determine FMC size according to table C.3
determine OCPD size according to 450.3(b)
I plan on using bonding bushings on each end of the primary side flex and terminating the EGC on the bushings as well as the ground points in the transformer and in the 480 panel.
secondary side:
I will size the conductors and the flex the same as above.
I will size the system bonding jumper according to table 250.66 as directed to by 250.30(a)1
I will size the GEC according to table 250.66 as directed by 250.30(a)3.
I am unsure as to what needs to be done about the size of the main disconnect in the 120/208 panel (3 feet away) and the grounding and bonding there also.
I know thats alot but I take my education and my raises seriously!
It is a small dry type (25kva I think) that is being fed from a 480 panel and feeds a 120/208 panel. I would appreciate if you guys could tell me if I am missing anything as far as procedure. The transformer will have FMC going to it on both sides.
Primary side:
determine feeder ampacity according to 215.2(B)1 (kva/480).
determine wire size according to 310.15(b)16
determine FMC size according to table C.3
determine OCPD size according to 450.3(b)
I plan on using bonding bushings on each end of the primary side flex and terminating the EGC on the bushings as well as the ground points in the transformer and in the 480 panel.
secondary side:
I will size the conductors and the flex the same as above.
I will size the system bonding jumper according to table 250.66 as directed to by 250.30(a)1
I will size the GEC according to table 250.66 as directed by 250.30(a)3.
I am unsure as to what needs to be done about the size of the main disconnect in the 120/208 panel (3 feet away) and the grounding and bonding there also.
I know thats alot but I take my education and my raises seriously!