1. I would install a 3 phase transformer readily available better balancing of the loads, but at this size...Well hardly an issue (depending on the size of the service and other 120 loads.

HAVING SAID THAT

240 VAC * 28 AMPS = 6,720 watts/1000 = 6.72 kw * 1.25 (at a minimum)8.4 kw which gives you a 10 KVA for a standard size.
 