For a high end residential setting what looks better? 6x6 or 8x8 trough/wireway? Keep in mind this is only used for 12 and 14 branch ckts above panels to allow cleaner access back into panels through 2" x 6" gal nipples into top of panels so 20 percent fill or derating isn't an issue.
All panels are flipped with lugs and feeders coming into a wireway/trough running under all panels then into a mdp.
I think the 6x6 trough looks a little less industrial however less space to get your hands in.
8x8 def has a wow factor but a bit over kill. Of course sanded plywood painted dark gray first.
 

·
Registered
Joined
·
6,189 Posts
Meh, I think 6x6 would be fine. It is just romex. You going to do cabinet grade plywood, or actually sand plywood?
 

·
Registered
Joined
·
414 Posts
Discussion Starter · #4 ·
Yes just two rows of 1/2" holes into to troff 1.5" on center. Second row in between first row. The Greenlee LS-50 battery powered punch is amazing. Also with punch no burs that you get when using a uni bit. Nicer on rx jackets
 

·
Registered
Joined
·
3,109 Posts
For a high end residential setting what looks better? 6x6 or 8x8 trough/wireway? Keep in mind this is only used for 12 and 14 branch ckts above panels to allow cleaner access back into panels through 2" x 6" gal nipples into top of panels so 20 percent fill or derating isn't an issue.
All panels are flipped with lugs and feeders coming into a wireway/trough running under all panels then into a mdp.
I think the 6x6 trough looks a little less industrial however less space to get your hands in.
8x8 def has a wow factor but a bit over kill. Of course sanded plywood painted dark gray first.
I've done 4x4 above a new basement sub-panel. There was only about a foot of wire below the floor joists to work with, much of it AL.

I even brought the aux gutter down to the panel with a Tee so I didn't have to worry about derating wire or conduit fill.

All the grounds were landed in the gutter, which didn't even have to be listed.

Even the inspector was impressed.

Go for it:thumbsup:
 

·
Registered
Joined
·
2,173 Posts
Electrical work is not art, many wish it wasn't something, But in most cases it's required.

Wireway troughs can be trickie. People generally don't understand nor comply with sizing per the application. I'm just saying!

Frankly I'm thinking of Grouped sevices here!

It's not a case where 20% is called out in respects to a nipple. it's 60%.

My belief is that where we go wrong on this type of install is to account for conduits sizing but miss on the exact amount of all the wires that are in a wireway/trough!

Running a 15/30 panel that's one thing, combining mutli 15/30's; first why bother and secondly that changes things.

The math wasn't presented.
 

·
Registered
Joined
·
8,050 Posts
I don't think it's practical for resi settings. As soon as you put 15 romexs in it you're shot
 

·
Registered
Joined
·
414 Posts
Discussion Starter · #8 ·
We are way under the 20 percent fill. And 192 wires as per rigid at 60 percent fill, that would never happen as there is a 2" nipple left and right of each panel leaving the panel.
 

·
Registered
Joined
·
414 Posts
Discussion Starter · #9 ·
I know what your saying about the not more than 30 conductor rule. That's why we use divider/ end caps in trough too
 

·
Registered
Joined
·
8,050 Posts
And what does that cap do in relation to ampacity in real life? Not a thing. Some of the ways to get around the code are just as ridiculous as the code itself
 

·
Registered
Joined
·
414 Posts
Discussion Starter · #13 ·
It keeps each section separate as to comply with 30 conductor rule. I'm certainly not concerned with real ampacity here as all heavy geo thermal AC compressor loads go directly to the mdp. Just lighting loads
 

·
Registered
Joined
·
3,450 Posts
What's the difference if you describe putting end caps in the middle of a gutter to circumvent code rules or you just post a pic of it?

Would that make it any less hokey?:no:
 

·
Registered
Joined
·
8,050 Posts
So is it generally agreed upon that sectioning off parts of the same gutter starts you back at zero for your cccs? I never heard of this practice before
 