Discussion Starter · #1 ·
Hi guys, just wondering are there code rule preventing running two independent circuit in one cable? I am thinking of running two 32A EV circuit in one teck 8/4C later in a junction box split into two teck 8/2 for nema 6-50.
 

· Registered
Construction Electrician
Joined
·
4 Posts
Discussion Starter · #4 ·
Yes I forgot the derating of more than 3 current carrying conductors. I think this is a old issue. So far I am getting away with 40A breaker with Nema 14-50 or Nema 6-50 receptacle in the greater Vancouver area (residential/commercial).
 