I need some advice and opinions please: I am in the position of making recommendations to a Client in a safety/inspection report.
The client has two UPS units plugged into a receptacle that is fed from the panel (To the UPS Input). Then at the UPS output they have a male cord-cap with cabtire/flexible cords plugged in, that enter the panel and are joined to two different circuits (#12AWG T90). These conductors were previously connected to breakers. The conductors are going into a slab conduit, then later surface EMT, and is shared with other circuits from that Panel. The UPS is feeding BAS System panels. I believe ESA has already called them out once for this, if I recall correctly, but I don’t know what the result or remedy was. (I have a photo if anyone needs to see the setup).
In my opinion I see this current setup unsafe, and goes against OEC:
6-212 (1) Enclosures for breakers not to be used as a junction box feeding through to other apparatus.
4-030 (2) to identify the neutrals of different systems; neutrals are not identified as different (they may even be sharing a neutral with another circuit but I didn’t check).
And 14-414 (4) – suitable warning of multiple sources.
Am I missing anything else? Please let me know if I am wrong or additions to any the above determinations. Or am I being too particular?
Thank you very much in advance!
First post on this great forum!
I need some advice and opinions please: I am in the position of making recommendations to a Client in a safety/inspection report.
The client has two UPS units plugged into a receptacle that is fed from the panel (To the UPS Input). Then at the UPS output they have a male cord-cap with cabtire/flexible cords plugged in, that enter the panel and are joined to two different circuits (#12AWG T90). These conductors were previously connected to breakers. The conductors are going into a slab conduit, then later surface EMT, and is shared with other circuits from that Panel. The UPS is feeding BAS System panels. I believe ESA has already called them out once for this, if I recall correctly, but I don’t know what the result or remedy was. (I have a photo if anyone needs to see the setup).
In my opinion I see this current setup unsafe, and goes against OEC:
6-212 (1) Enclosures for breakers not to be used as a junction box feeding through to other apparatus.
4-030 (2) to identify the neutrals of different systems; neutrals are not identified as different (they may even be sharing a neutral with another circuit but I didn’t check).
And 14-414 (4) – suitable warning of multiple sources.
Am I missing anything else? Please let me know if I am wrong or additions to any the above determinations. Or am I being too particular?
Thank you very much in advance!