I had a vfd running a 25 hp motor that faults on overcurrent.it faulted while stopping. What would I look for and how would I reset the fault?
Without knowing a lot more about the VFD in question and how it is being used, it's hard to help. If for example your drive is set up for Dynamic Braking, you could be exceeding the DB current. If set up for Decel but there is there is a mechanical brake that engages as soon as you hit the Stop button, then it will be trying to continue to drive the motor against the brake. If it is set up for Coast to Stop, it should never trip on stopping so it may indicate an electrical problem such as a short. Resetting it will be described in the instruction manual.I had a vfd running a 25 hp motor that faults on overcurrent.it faulted while stopping. What would I look for and how would I reset the fault?
Read it from the VFD display. Most meters will not display current correctly looking at the PWM output of a VFD.how would I measure the current if the vfd is running at 90 hz
Does anyone know if this is a new feature for small drives? Which manufacturers? I don't recall ever seeing this as a feature on the drives I worked on. I'm wondering if this could be a feature that failed on some small Allen Bradley Kinetix drives of ours recently. The overcurrent protection software model was allowing the drives to destroy themselves. 4 drives later the AB engineer came in and saw it fail and said essentially "yeah, it shouldn't do that".The drive will automatically lower the amp rating because the cooling fan on the end of the motor is not running as fast.
These drives that I was talking about I think we're Emerson drives. They were 50 hp. This feature is common with all drives. It is automatically done by the drive. We have applications where we run vfds very slow and we have to find the parameter to boost the output voltage at low hertz to cut down on the amps. Everything from 250 hp drives to 1hp.Jabberwoky said:Does anyone know if this is a new feature for small drives? Which manufacturers? I don't recall ever seeing this as a feature on the drives I worked on. I'm wondering if this could be a feature that failed on some small Allen Bradley Kinetix drives of ours recently. The overcurrent protection software model was allowing the drives to destroy themselves. 4 drives later the AB engineer came in and saw it fail and said essentially "yeah, it shouldn't do that".
Oh yeah that's torque boosting. I thought you were talking about a feature that reduced amperage entirely for operating temperature control.These drives that I was talking about I think we're Emerson drives. They were 50 hp. This feature is common with all drives. It is automatically done by the drive. We have applications where we run vfds very slow and we have to find the parameter to boost the output voltage at low hertz to cut down on the amps. Everything from 250 hp drives to 1hp.