Have a customer with voltages drop problem(By they way Hello everybody , im new to the site(John ), Get right to it,they have a 800amp service 208 volt3 phase.the feeder from the Ct cabinet is about 360' long,with 4 4/0 alu per phase/ use , their amp draw is about 212 per phase from power company's single leg. I have about three different ideas about correcting this,Iwould like to get some input from you guys ,thanks
 

·
Registered
Joined
·
11 Posts
Discussion Starter #5
Voltage drop problem

Have a customer with voltages drop problem(By they way Hello everybody , im new to the site(John ), Get right to it,they have a 800amp service 208 volt3 phase.the feeder from the Ct cabinet is about 360' long,with 4 4/0 alu per phase/ under ground , their amp draw is about 212 per phase from power company's single leg. I have about three different ideas about correcting this,Iwould like to get some input from you guys ,thanks
 

·
Registered
Joined
·
11 Posts
Discussion Starter #11
What they did is buried the first 250 and the last 110 is in conduit 6" under a road
First idea is to run 4 4" pvc to pull box 250 ,and splice into 4/0 s
 

·
Registered
Joined
·
11 Posts
Discussion Starter #12
What they have is a ct with trough on top and 4 4" stubed in the ground im thinking 2 foot deep , havent dug up yet , then after 250 foot they have a 6" pvc acrossed the road about 110 ' long to 800 amp mdp.Buy the way thank for the intro.
 

·
Town Drunk
Joined
·
3,725 Posts
Welcome! :thumbsup:
 

·
Registered
Joined
·
31,133 Posts
Buck boost transformer.

Transformer 1.73 to 1 with taps set high. (208 delta to 208/120 wye)

More conductors .
 

·
Registered
Joined
·
71 Posts
are you sure that 212 A is the full load ? (service way oversized or is there allowance for future ?)

anyway, if my math is right, using cmils = 1.732 k I D/Vd =1.732x21.4x212x360/ (3% of 208=6.24) = 464000. for four sets of AL that's only 116000 which is 2/0.

So I guess my question is, is there really a voltage drop problem with this portion of the system, or maybe somewhere else ?
 