MWBC = don't be taking neutrals apart if you don't know what's connected to them!
MWBC = don't be taking neutrals apart if you don't know what's connected to them!So me and my Jman got into a HR box with 2 circuits. He turned off the breakers and undid the joints. There was a load on the neutral when he undid the joint. I put my ticker in the box and was picking up voltage on the neutral. We used a meter and got 230v. This was on the neutral wire that would be continuing downstream, not back to the panel.
What could cause this? Isn't the neutral supposed to have no voltage on it? Just the unbalanced load? Considering that everything is properly bonded at the transformer?
Correct....if you unplugged or disconnected every load that the neutral is connected to then it will be dead with the exception of possible phantom voltage readings.So by undoing the neutral, if anyone had tied something in downstream and shared that neutral then you could read voltage correct? Since the joint is broke and the potential to ground has been removed?
I don't know whats causing the problem, but I do know never, never, never open a neutral with the power on if it's multi wire branch circuit. You could possibly send a back feed through other appliances connected to the circuit and BLOW UP anything connected to the circuits. I've seen it happen by mistake! Pulling a splice out of a box, one neutral a little shorter than the others, splice not tight (spliced by others) and it pulled out of the joint. POOF! Can be a very expensive lesson!So me and my Jman got into a HR box with 2 circuits. He turned off the breakers and undid the joints. There was a load on the neutral when he undid the joint. I put my ticker in the box and was picking up voltage on the neutral. We used a meter and got 230v. This was on the neutral wire that would be continuing downstream, not back to the panel.
What could cause this? Isn't the neutral supposed to have no voltage on it? Just the unbalanced load? Considering that everything is properly bonded at the transformer?
Not true, actually any neutral with a load on the system will have voltage on it (depending where you measure the voltage, when measured to the EGC. There is ALWAYS voltage drop on any conductor between the source and a load, the neutral is bonded at the main service or separately derived system, the further you get from this point, with load on the system there will be an increasing voltage due to the VD.A true neutral will have no voltage on it.
A true neutral with no voltage means no power. You cannot have power without voltage. Current does not flow without voltage.A true neutral will have no voltage on it.. but what we usually call a neutral (because it's the white noodle) is really just a return for the hot conductor. It's the load side of the hot conductor. If you open that while voltage is still being supplied on the line side, you can let the smoke out of electronics.
What is the system voltage? You measured 230 volts between which conductors? How many breakers did he open? Which joints did he take apart?So me and my Jman got into a HR box with 2 circuits. He turned off the breakers and undid the joints. There was a load on the neutral when he undid the joint. I put my ticker in the box and was picking up voltage on the neutral. We used a meter and got 230v. This was on the neutral wire that would be continuing downstream, not back to the panel.
What could cause this? Isn't the neutral supposed to have no voltage on it? Just the unbalanced load? Considering that everything is properly bonded at the transformer?
Think of a light bulb, 120 volt on one side and neutral on the other side if you disconnect that neutral it will become hot. It gets more complex but I think this is a better way of explaining it loltravis13 said:So me and my Jman got into a HR box with 2 circuits. He turned off the breakers and undid the joints. There was a load on the neutral when he undid the joint. I put my ticker in the box and was picking up voltage on the neutral. We used a meter and got 230v. This was on the neutral wire that would be continuing downstream, not back to the panel. What could cause this? Isn't the neutral supposed to have no voltage on it? Just the unbalanced load? Considering that everything is properly bonded at the transformer?
If you touch that neutral, you will not be too happy.
I bet you holla'd like a little bish.The worst I ever got bit in my entire life, save 277, was from an open neutral serving a fluorescent ballast. That sheet hurt.
I feel the need to point out that there must be 2 points in order to get a voltage reading. You only mentioned one point, the neutral wire, so now we have to assume the 2nd point.We used a meter and got 230v. This was on the neutral wire that would be continuing downstream, not back to the panel.