When is it required to be grounded? Is it only when the AHJ requires it?
the table show how to size, but where does the code ask for it to be grounded?If the water pipe is metal coming into the structure it is required to be bonded to the service(table 250.66), gas pipe is also required to be bonded to service. If there is csst gas pipe bond according to manufacturer's installation instructions, if the gas pipe is all black iron or galvanized, the equipment grounding conductor for the appliances likely to energize it are considered a sufficient bond.
Sent from my XT1055 using electriciantalk.com mobile app
250.50 and 250.52carryyourbooks said:the table show how to size, but where does the code ask for it to be grounded?
Is your water heater plumbed in copper?carryyourbooks said:herein lies my question. i have water coming into my house via pvc on the opposite side of the house from the panel. my house is plumbed in pex. there is a copper spigot sticking out of the house that is connected to pex. should a ground wire be run to the spigot? i have a ground run to the gas line and rebar.
No. The chances of that spigot becoming energized is very very unlikely. Plus, how would you bond it anyway?carryyourbooks said:herein lies my question. i have water coming into my house via pvc on the opposite side of the house from the panel. my house is plumbed in pex. there is a copper spigot sticking out of the house that is connected to pex. should a ground wire be run to the spigot? i have a ground run to the gas line and rebar.
yes. and there is a #6 ran from water heater to water heater. (i have 2 water heaters)Is your water heater plumbed in copper?
i live in a tract home. they bonded it by running a #6 to the clamp which is outside the brick.No. The chances of that spigot becoming energized is very very unlikely. Plus, how would you bond it anyway?
I Was talking about water piping not the gas piping. And yes, by code the article I posted tells you not to use gas piping as an electrodeAdam12 said:The code only asks for it to be bonded if it's likely to be energized. 250.104 B. Any appliance, furnace, etc that uses gas makes it "likely to become energized". Therefore it must be bonded. However the EGC for these is acceptable as a bonding means. 250.50 & 250.52 don't ask for it to be bonded. 250.52 B1 tells you not to use it as a grounding electrode.
That is one of my favorite stupid code statements.The code only asks for it to be bonded if it's likely to be energized. 250.104 B.
.
It's required to bond the gas pipe if csst is used in a house. BOND not GROUNDSkooby said:Around here inspections have only been done for a few years, some EC's in the 70's+80's never drove ground rods; and the HVAC guys are just running a #6 from the gas meter to service panel ground bus any time they do work on a furnace and run any csst. In effect turning the incoming gas line into an electrode.... Sent from my XT1055 using electriciantalk.com mobile app
Only is it's yellow csst, the new black stuff aka counter strike doesn't required the extra bond.ElectricJoeNJ said:It's required to bond the gas pipe if csst is used in a house. BOND not GROUND