Discussion Starter · #1 · (Edited)
Working on a job that has welded wire mesh instead of rebar in every concrete pad for switchgear and transformers, etc. The wire only has a diameter of .192" inches. It has to be bonded to the ground ring (4/0) and I'm trying to figure out what type of lug or crimp to use.

Having trouble finding something that matches that wire range. Any suggestion appreciated
 

· Registered
Joined
·
6,229 Posts
I don't have a code book in front of me, but I thought concrete encased electrodes had to be of a certain size (3/8 or 1/2" maybe?) and have 20 linear feet within the concrete. Don't think you have to bond wire mesh.
 

· Electrical Simpleton
Joined
·
3,343 Posts
I don't have a code book in front of me, but I thought concrete encased electrodes had to be of a certain size (3/8 or 1/2" maybe?) and have 20 linear feet within the concrete. Don't think you have to bond wire mesh.
I'm guessing this is a job spec. I agree with you it is not an NEC requirement.

Pete
 

· Mad Skills
Joined
·
5,798 Posts

· Registered
Joined
·
3,451 Posts
I see these split-bolts are rated:
"For use with copper conductor types: Solid, Compact,
Compressed, Concentric"
....I don't see where it says for steel mesh/rebar.

Am I reading it wrong?
To be honest, I never looked into it any further. Our inspector here only required grounding/bonding and db rated. These seemed to fit the bill and he approved them.

If someone knows of something else that specifically states it's for wire mesh I'd be interested in knowing as well.
 