Switching 2 hot conductors off at the same time.
The main breaker in a 120/240 panel is a double pole switch. Or the disconnect.. or a switch for a 208/240V motor. Lots of situations.
Under the NEC we are always allowed to switch the neutral if the hots are switched at the same time.i belive the neutral is allowed to switched with the hot at places like a gas pump.:whistling2:
Thanks. I was asking because the picture shows a neutral being switched, though someone has said that is permitted in certain situations. I don't know the reason why it would be done, though.FrunkSlammer said:Switching 2 hot conductors off at the same time.
The main breaker in a 120/240 panel is a double pole switch. Or the disconnect.. or a switch for a 208/240V motor. Lots of situations.
I have never worked with one of these. I'm assuming you just bring both 120 legs to it, so the double pole is used to switch them both off, correct?B4T said:Think of a switch for a 240V. pool pump motor...
Why are you assuming it is a neutral?Thanks. I was asking because the picture shows a neutral being switched,.
someone has said that is permitted in certain situations.
404.2 Switch Connections.
(B) Grounded Conductors. Switches or circuit breakers shall not disconnect the grounded conductor of a circuit.
Exception: A switch or circuit breaker shall be permitted to disconnect a grounded circuit conductor where all cir-cuit conductors are disconnected simultaneously, or where the device is arranged so that the grounded conductor can-not be disconnected until all the ungrounded conductors of the circuit have been disconnected.
It's sometimes required.I don't know the reason why it would be done, though
More or less, but I would not call them '120 legs' I would just call it a 240 volt circuit.I have never worked with one of these. I'm assuming you just bring both 120 legs to it, so the double pole is used to switch them both off, correct?
More or less, but I would not call them '120 legs' I would just call it a 240 volt circuit.
It depends, do you want people to think you know what you are talking about or not?Does it matter?:whistling2:
. .(2011)
404.2
(b) grounded conductors. Switches or circuit breakers
shall not disconnect the grounded conductor of a circuit.
exception: A switch or circuit breaker shall be permitted to disconnect a grounded circuit conductor where all circuit conductors are disconnected simultaneously, or where the device is arranged so that the grounded conductor can- not be disconnected until all the ungrounded conductors of
the circuit have been disconnected.
404.8
(c) multipole snap switches. A multipole, general-use snap switch shall not be permitted to be fed from more than a single circuit unless it is listed and marked as a two- circuit or three-circuit switch, or unless its voltage rating is not less than the nominal line-to-line voltage of the system supplying the circuits.
It depends, do you want people to think you know what you are talking about or not?
It's like calling it 110 volts.
I can't say a and b phase on a single phase system? Well how do I describe it when I buck em hard?meadow said:I don't see legs as a DIY term, rather slang used to describe something. Phase on a single phase service technically isn't right either but many electricians refer to it as such.
We are all free to do what we please.:thumbsup:I don't see legs as a DIY term, rather slang used to describe something.