I'm asking about the middle switch of these three. Why would this be used as opposed to a single pole? Doesn't this picture show a switched neutral, which the Code prohibits? Thanks in advance.

 

· IBEW L.U. 1852
Joined
·
5,250 Posts
Switching 2 hot conductors off at the same time.

The main breaker in a 120/240 panel is a double pole switch. Or the disconnect.. or a switch for a 208/240V motor. Lots of situations.

Stop answering guys............its perfectly explained.:thumbsup::laughing:
 

· Banned
Joined
·
746 Posts
"what is a double pole switch used for"?

:laughing::laughing::laughing:
 

· Registered
Joined
·
364 Posts
Discussion Starter · #9 ·
FrunkSlammer said:
Switching 2 hot conductors off at the same time.

The main breaker in a 120/240 panel is a double pole switch. Or the disconnect.. or a switch for a 208/240V motor. Lots of situations.
Thanks. I was asking because the picture shows a neutral being switched, though someone has said that is permitted in certain situations. I don't know the reason why it would be done, though.
 

· Salty Member
Joined
·
31,030 Posts
Thanks. I was asking because the picture shows a neutral being switched,.
Why are you assuming it is a neutral?

someone has said that is permitted in certain situations.
404.2 Switch Connections.


(B) Grounded Conductors. Switches or circuit breakers shall not disconnect the grounded conductor of a circuit.

Exception: A switch or circuit breaker shall be permitted to disconnect a grounded circuit conductor where all cir-cuit conductors are disconnected simultaneously, or where the device is arranged so that the grounded conductor can-not be disconnected until all the ungrounded conductors of the circuit have been disconnected.
I don't know the reason why it would be done, though
It's sometimes required.
 

· Bilge Rat
motors and controls.........
Joined
·
10,045 Posts
I've used 2 pole switches to control 208 or 230 volt 3ø motors with built-in thermals.

Now before you jokers go and get your tails in a knot and rip me apart for violating the code at least 100 times, 430.84 plainly states that a controller need not open all conductors.

Note that it says 'controller' and not 'disconnect'.

Sure, it could be construed as hack, but it is absolutely code compliant provided the switch is rated for the voltage and HP of the motor it controls.

I will be out of town for a few days, so go ahead and rip me while I'm gone. I'll reply when I get back....
 

· animal lover /rat bastard
Joined
·
13,504 Posts
(2011)

404.2
(b) grounded conductors. Switches or circuit breakers
shall not disconnect the grounded conductor of a circuit.

exception: A switch or circuit breaker shall be permitted to disconnect a grounded circuit conductor where all circuit conductors are disconnected simultaneously, or where the device is arranged so that the grounded conductor can- not be disconnected until all the ungrounded conductors of
the circuit have been disconnected.

404.8
(c) multipole snap switches. A multipole, general-use snap switch shall not be permitted to be fed from more than a single circuit unless it is listed and marked as a two- circuit or three-circuit switch, or unless its voltage rating is not less than the nominal line-to-line voltage of the system supplying the circuits.
. .
 

· Licensed Journeyman
Joined
·
5,870 Posts
meadow said:
I don't see legs as a DIY term, rather slang used to describe something. Phase on a single phase service technically isn't right either but many electricians refer to it as such.
I can't say a and b phase on a single phase system? Well how do I describe it when I buck em hard?
 