Hi,
I work in an industrial setting were we have a couple hundred electrical motors. Most are 3 phase 460 volt 2 to 25 hp. Most are relatively new, about 2 to 5 years old. We have a lot of motor failures but they are generally mechanical failures not electrical.
The procedure is to basically wait until a motor fails and quickly replace it. I am trying to get beyond that mentality and gather some data on a few troublesome 20-25 h/p 3 phase 460 volt motors that have had electrical issues in the past.
I bought a Megohm meter. Actually I bought 3 of them but the first two were very cheap Chinese Biddle knock offs. I finally found an excellent condition older Biddle meter. It is a 500 volt/ 200 meg hand cranked.
My question is, everything I meg reads infinity or at least over 200 megs. I guess that is good if the readings are correct but I expected some variance. When I take my readings I
Disconnect all three lines from the motor, Connect the earth line to the motor grounding lug or frame. Attach the line the one of the motor line connections. Cranky furiously for 30 seconds to one minute and check the readings while I am turning the crank. Nothing reads below infinity. When I was using the Chinese meters I was getting the same results but these read to 500 megs. I was still reading infinity. Are these results normal or am I doing something wrong?
Also I would like to check some hard to get to motors from the motor control cabinet. These motors are connected to vfd’s. I would kill the power going to the cabinet and disconnect the lines coming from the vfd to the motor and test these lines from line to ground. I suspect the readings might be artificially low but would this be a decent indication of the motor’s health if the readings were normal?
Last question, this meter does not have a discharge switch. Would it be acceptable to connect the motor leads to ground for a few minutes after the test to make sure there is no built up voltage.
Thanks for any advice.
I work in an industrial setting were we have a couple hundred electrical motors. Most are 3 phase 460 volt 2 to 25 hp. Most are relatively new, about 2 to 5 years old. We have a lot of motor failures but they are generally mechanical failures not electrical.
The procedure is to basically wait until a motor fails and quickly replace it. I am trying to get beyond that mentality and gather some data on a few troublesome 20-25 h/p 3 phase 460 volt motors that have had electrical issues in the past.
I bought a Megohm meter. Actually I bought 3 of them but the first two were very cheap Chinese Biddle knock offs. I finally found an excellent condition older Biddle meter. It is a 500 volt/ 200 meg hand cranked.
My question is, everything I meg reads infinity or at least over 200 megs. I guess that is good if the readings are correct but I expected some variance. When I take my readings I
Disconnect all three lines from the motor, Connect the earth line to the motor grounding lug or frame. Attach the line the one of the motor line connections. Cranky furiously for 30 seconds to one minute and check the readings while I am turning the crank. Nothing reads below infinity. When I was using the Chinese meters I was getting the same results but these read to 500 megs. I was still reading infinity. Are these results normal or am I doing something wrong?
Also I would like to check some hard to get to motors from the motor control cabinet. These motors are connected to vfd’s. I would kill the power going to the cabinet and disconnect the lines coming from the vfd to the motor and test these lines from line to ground. I suspect the readings might be artificially low but would this be a decent indication of the motor’s health if the readings were normal?
Last question, this meter does not have a discharge switch. Would it be acceptable to connect the motor leads to ground for a few minutes after the test to make sure there is no built up voltage.
Thanks for any advice.