Switched said:
Whatever happened to "The only stupid question is the one you didn't ask"? Maybe it's been years since he's hooked one up and wants to double check himself before he effs it up.
I helped out didn't I.
 

·
Bilge Rat
motors and controls.........
Joined
·
7,086 Posts
If its 120/240 secondary, he would need to ground x2 the center tap, since x1 & x4 are the ungrounded conductors.
If it's 120/240 3ø, then it's a high-leg ∆ system.

Typically, X3 is the high leg, and X4 is the neutral, but not always.

If possible, power it up with nothing connected to the secondary side and measure voltages. You should have 120 from X4 to X1 as well as X4 to X2, and 208 from X4 to X3.

240 should be present from X1 to X2, X2 to X3, and X3 to X1.

If so, ground X4; it is the neutral.
 

·
Premium Member
Joined
·
18,554 Posts
I am installing a 3 phase 480/277 primary to 240/120 secondary. I have x1, x2, x3, x4. is the x4 the one to bond to ground?
You are going delta/delta.
One of the transformers are center tapped. You might be able to physically see it.
If not, don't take a chance, fire it up and see what voltages you have.
One of them will give you 120/120/208. This will be the center tapped one, all others will be 240 to each other.
 

·