Load diversity.200A cable neutral is 3/0, hots are 4/0. 100A is 2 #2s, and a #4 for the neutral. Why is this allowed in service cable, but not in the interior wiring in a home?
Even then, one some services the predominate loads are 240 which means they force the hots to be well upsized to what the 120s need. So even with everything 120 running on one leg (near impossible) it still might not approach the undersized neutral rating.Load diversity.
On a branch circuit, you can have full-load on one side of the MWBC, and zero on the other. This means the neutral must be capable of carrying the full load current.
It's a different story with a service. First, it's rare that the service runs at 100% of it's rating, and highly improbable that that 100% is all on one hot leg.
I think you mean GEC, not EGC.:thumbsup:Some code articles actually allow you to have a neutral only as big as the EGC be loading permits it.
I think you mean GEC, not EGC.:thumbsup:
What's MWBC?480sparky said:Load diversity.
On a branch circuit, you can have full-load on one side of the MWBC, and zero on the other. This means the neutral must be capable of carrying the full load current.
It's a different story with a service. First, it's rare that the service runs at 100% of it's rating, and highly improbable that that 100% is all on one hot leg.
Multi wire branch circuitWhat's MWBC?
Multi wire branch circuit