Yesterday I had an emergency call for a 34.5 Wye (3-wire) to 208/120 Wye (4-wire) Transformer, with secondary voltage issues.

While this had nothing to do with the problem I had it is a question I have regarding the transformer


Typically distribution transformers we deal with are Delta/Wye, I have run across this before at higher voltages a few times in the past and was wondering is there an advantage to a Wye/Wye at higher voltages?

The voltage issue with the transformer in question was an open secondary winding.
 

·
Donuts > Fried Eggs
Joined
·
17,042 Posts
That's actually what I thought this was gonna be about.

The Why's of Wyes.


The biggest reason I know that utilities like wye-wye connections is it eliminates any possibility of ferroresonance when it's switched by single cutouts. The only other way to protect against that is to put in a gang switch that opens all the lines at once, or to put in chain grounds on one of the delta phases.