Do they not sell T+B bakelite 4" square deep junction boxes (screw on type with no bracket) north of the Mason Dixon line?
 

· electrorick
Joined
·
329 Posts
The topics covered on this site include activities in which there exists the potential for serious injury or death.

ElectricianTalk.com DOES NOT
 

· animal lover /rat bastard
Joined
·
13,504 Posts
I've often thought that small transformers were probably less of a fire hazard inside the box than outside, except that the cover should be vented for heat dissipation. However, without a barrier your install is a violation, so no matter how the fire started you are on the hook; for that reason (liability) I wouldn't do that. If you relabeled the transformer "class 1" and used nm for the LV side, I'd say it was compliant. I like the class2 transformers that have built in short ckt and overload protection.
 