Would you use this for a 100 amp service riser?

4K views 25 replies 10 participants last post by  Chrisibew440 
#1 ·
Would you use this in a raceway that is located in a wet location?



I am going to say no.
 
See less See more
1
#3 ·
What about 310.8(C)?
(C) Wet Locations. Insulated conductors and cables used
in wet locations shall comply with one of the following:
(1) Be moisture-impervious metal-sheathed
(2) Be types MTW, RHW, RHW-2, TW, THW, THW-2,
THHW, THWN, THWN-2, XHHW, XHHW-2, ZW
(3) Be of a type listed for use in wet locations
1 and 3
 