150 amp vs 200 amp service.

19K views 3 replies 3 participants last post by  MikeFL  
150A sounds lean for everything you have planned. You really need to a do a proper load calculation. Do you have piped nat gas?

150A is still a worthwhile upgrade. It uses 200A gear with a smaller main breaker. The one thing I recommend is for the meter-to-main-breaker wire, and ground wire, be sized for 200A to make the eventual upgrade easier.

Resale should be better than with a 100A FPE main.
 