Dryer Receptacle

6K views 36 replies 18 participants last post by  Dennis Alwon  
It'd be better to land it on the neutral bus rather than the ground bus. The reason is if the ground wire gets disconnected anywhere between the panel and the neutral-ground bond, and the dryer is running or trying to run, everything grounded will be 120 volts above the actual ground.

If it's landed on the neutral bus, the only thing that could get energized is the dryer frame.

But the actual reality is it needs to be 4 wire.