This is one of those things in which it's only against code because people were bored and wanted to make more rules. And people only follow it because they need to feel warm and safe by following someone else's orders.
 
This is one of those things in which it's only against code because people were bored and wanted to make more rules. And people only follow it because they need to feel warm and safe by following someone else's orders.
This is not a new code for us. It came out in 1972. Knob and tube wasn't getting installed since the 50's so this code came along with the new multi conductor cables that were being used.
 
You can not run separate wires. All the wires for a circuit must be contained in the same multi conductor cable. 12-106(1)
All the wires required for a 3-way switch circuit are 2 travellers and either a hot or a switch leg. The switch location requires a neutral, the switch circuit does not.
 
All the wires required for a 3-way switch circuit are 2 travellers and either a hot or a switch leg. The switch location requires a neutral, the switch circuit does not.
What are you saying?

the switch location requires a neutral not the actual switch, sure, but how do you plan on getting the neutral to the location? The neutral is part of the circuit. There is no such thing as "the switch circuit".

Code specifies they all must be contained in the same cable. You can not run some of the wires in one cable and the other ones in another cable to the same location.
 
LOL, I carry the bare minimum since I only do resi service work, and those 3 are exactly what I carry.



I also have about 100' of 12-3 that has been sitting there for a couple years. And then 4 500' reels of #12 (green, white, black, red).
Anytime i see someone buy less then a 250' roll of romex I get a chuckle. A 25' full and I'm laughing out loud.

Sent from my SM-G950U using Tapatalk
 
What are you saying?

the switch location requires a neutral not the actual switch, sure, but how do you plan on getting the neutral to the location? The neutral is part of the circuit. There is no such thing as "the switch circuit".

Code specifies they all must be contained in the same cable. You can not run some of the wires in one cable and the other ones in another cable to the same location.

I didn't say that. The code requires a neutral at each switch location.



What would be wrong with this? We've always ran s wires between switches.
 
Instead of name calling, how about posting a pic of how you would wire them? WITHOUT 4 wire cable. Just so nothing gets lost in the translation.
 
What are you saying?

the switch location requires a neutral not the actual switch, sure, but how do you plan on getting the neutral to the location? The neutral is part of the circuit. There is no such thing as "the switch circuit".

Code specifies they all must be contained in the same cable. You can not run some of the wires in one cable and the other ones in another cable to the same location.

I didn't say that. The code requires a neutral at each switch location.

View attachment 135100

What would be wrong with this? We've always ran s wires between switches.
What is wrong with it is It is against code.

12-106 Multi- and single-conductor cables
1) Where multi-conductor cable is used, all conductors of a circuit shall be contained in the same multi-conductor cable.
 
Instead of name calling, how about posting a pic of how you would wire them? WITHOUT 4 wire cable.
Easy. Feed the first switch, run a three wire from first switch to second switch, then a two wire from the second switch to the load. No 4 wire needed and each switch location has a neutral
 