Here is the specs I have been given for a machine from the EU coming to the USA.
If you use a high-leg delta connection (see the previous picture), you have 3 phase and 1 neutral and 1 ground. If you measure the voltage between phase and phase you get 480V. It is good, but if you measure the voltage between 1 phase and neutral you need to measure 240V. If you measure more you need to reduce the inlet 480V to 400V. Originally our machine works well on 400V, but each phase is no more, than 240V.
In the diagram (which I can not upload) they show a delta with ABC and then a separate G and N which are drawn connecting to the delta. This is not Wye
We have 480v 3 Phase from the main but this is 3 wire and then units are grounded.
Can this service be a High Leg Delta or do I need a transformer and then 5 wires?
If you use a high-leg delta connection (see the previous picture), you have 3 phase and 1 neutral and 1 ground. If you measure the voltage between phase and phase you get 480V. It is good, but if you measure the voltage between 1 phase and neutral you need to measure 240V. If you measure more you need to reduce the inlet 480V to 400V. Originally our machine works well on 400V, but each phase is no more, than 240V.