Service call for small new machine shop:
-multiple ckts tripping in grinding/abrasive room
-I made a list of equipment being used and piped out 6 new ckts where there was one before
- this whole shop is an upstart, with mostly tools from harbor freight
- there were 2 harbor freight dust collectors with no nameplate on the motor (voltage and freq only), with factory 15 A cords, I put them both on one of the new 20A ckts
-a week later that ckt tripped, so I finally looked up that pos on the harbor freight website and found that it is a 2hp motor with 20FLA
-the website says that it is UL listed
-a 2hp motor requires 24FLA in the NEC (30A of conductor)
-this thing comes with a 15A plug
My question is would you size the ckt to the motor, or put each on their own 20A brkr. (How is this UL listed?)