One minute is in the standards.

This does two things. The first thing is to wait long enough to charge up the system capacitance. The line is or should be insulated from ground, forming a capacitor. This contains no useful diagnostic information so we just want to charge it to get it out of the way. This is usually over in a few seconds to tens of seconds.

The second is so that if we both run the test we get consistent results.

PI does a 10 minute and 1 minute test and takes the ratio. After the system capacitance is charged individual molecules in the insulation slowly align themselves to the field, increasing resistance further. PI uses this like a yard stick. Typicallly PI is 2-6. If it’s low you have a failure. High indicates test problems or cracked insulation.

IEED is kicking around making the Megger test graphical since that tells you more than an absolute number.