Hey Guys got a question when you are sizing an overload for a motor and you can't find the exact size do you go the next step up or the next step down? Settle a argument!
Yeah, I agree. The ranges generally overlap, it shouldn't be possible to not have a heater element that will not cover your nameplate FLA.Never go over, going under is fine. But it's based on the loading.
Keep in mind that o/l's have a range,, so it's hard to think you can't get the proper size.
What do you have and what amperage do you need?
The following is for motors rated for Continuous Duty:
For motors with marked service factor of not less than 1.15, or motors with a marked temperature rise not over +40 °C (+104 °F), apply application rules 1 through 3. Apply application rules 2 and 3 when the temperature difference does not exceed +10 °C (+18 °F). When the temperature difference is greater, see below.
1. The Same Temperature at the Controller and the Motor — Select the “Heater Type Number” with the listed “Full Load Amperes” nearest the full load value shown on the motor nameplate.
2. Higher Temperature at the Controller than at the Motor — If the full load current value shown on the motor nameplate is between the listed “Full Load Amperes”, select the “Heater Type Number” with the higher value.
3. Lower Temperature at the Controller than at the Motor — If the full load current value shown on the motor nameplate is between the listed “Full Load Amperes”, select the “Heater Type Number” with the lower value.
[/QUOTE]JRaef said:Yeah, I agree. The ranges generally overlap, it shouldn't be possible to not have a heater element that will not cover your nameplate FLA.
But as to never going over, that will depend, and this may be where your friend is getting his info. The old rule of thumb is that you cut the motor life by 50% for every heater size over the correct one. But selecting the correct one has a LOT to do with what TYPE of OL relay you have. Most, but not all, bi-metal overload relays are what is called "ambient compensated" or "ambient insensitive". That means that it doesn't matter (much) if the OL relay (starter) is in an area where the ambient temperature is different from the motor. But for those that are NOT ambient comp./insensitive, and for eutectic melting alloy (solder pot) OL relays, then there are rules about how the heaters should be selected based upon the different ambient conditions. Here is what A-B says about it regarding the Type W eutectic alloy type heater elements:
The following is for motors rated for Continuous Duty:
For motors with marked service factor of not less than 1.15, or motors with a marked temperature rise not over +40 °C (+104 °F), apply application rules 1 through 3. Apply application rules 2 and 3 when the temperature difference does not exceed +10 °C (+18 °F). When the temperature difference is greater, see below.
1. The Same Temperature at the Controller and the Motor — Select the “Heater Type Number” with the listed “Full Load Amperes” nearest the full load value shown on the motor nameplate.
2. Higher Temperature at the Controller than at the Motor — If the full load current value shown on the motor nameplate is between the listed “Full Load Amperes”, select the “Heater Type Number” with the higher value.
3. Lower Temperature at the Controller than at the Motor — If the full load current value shown on the motor nameplate is between the listed “Full Load Amperes”, select the “Heater Type Number” with the lower value.
Are you sure? I was always instructed to use the FLA to size the OL. I use FLA x 1.25 to size the conductors and the OCP, but not the "heaters".Assuming the motor in question is continuous then sizing overloads is pretty simple.
FLA x 1.25
Heater coils are rated to protect standard 40°C rise motors, and open and drip proof motors having a service factor of 1.15 at approximately 125% of rated motor current, and where controller and motor are at same ambient.