Siemens 100amp panel guts replacement

2.6K views 18 replies 12 participants last post by  Signal1  
#1 ·
Does anyone here know if the panel guts of a newer residential Siemens EQ 32 cct panel will fit the older Siemens panels?
The existing panel is 23 years old.
Looks like its going to be a direct fit but not entirely sure.
No need to suggest replacing the entire panel, I know it's an option and I will obviously have to go that route if I cant replace the guts.
The first two photos are of the original EQ panel that needs the main breaker and bus bar replaced.
The last two photos are of a brand new Siemens 32 cct EQ panel.
 

Attachments

#3 ·
Are the stabs adjacent to the main bent on purpose on those panels? I've never seen that before. It sure looks like it will fit but you never know until you try.
 
#13 ·
I learned many years ago wiring large dust collectors and paint booths, that a air pressure difference as well as a temperature difference between inside and outside could cause large amounts of airflow through the conduit system.
Large airflow with a temperature difference at each end can make a huge amount of condensation inside the conduit, and in very short order under the right conditions.
I had jobs where a NEMA 4 large pushbutton enclosure totally filled with water in one weekend of operation.
Just from condensation alone, all of the conduit fittings were caulked from the outside with roofing caulk.
It taught me to never leave a conduit unsealed even for a short period.
If I didn’t have enough duct seal, at startup I would find a plastic bag to wad up and pack at both ends of the conduit, inside and outside, for a temporary seal till the system was proven good and totally functional.
Then the plastic bags could be easily pulled out and replaced with duct seal for a permanent fix.

same thing can happen with SE or SER service cable going from inside to outside, after having water pouring into a new main breaker, I learned to splay out the SE strands in the meter can and caulk the cable shut.
Lesson learned, and many future problems prevented.
 
#17 ·
I'd think that NEC has something similar to this ?

1/4" hole drilled at the bottom of the LB outside where it enters in the building.

As Frankendodge said, the Ductseal should be outside.

Image
 
#18 ·
We don't always have an LB at a wall penetration, many times in industrial situations the conduit passes straight thru the barrier wall or roof, and similar applies if your using SE cable or flexible seal tight conduit for a penetration. But if there is an LB or box, some drain or vent holes always makes practical sense. I always sealed both ends of s conduit run when there is a difference of air pressure or temperature at both ends.