What is the special requirements for a dental office

31K views 13 replies 10 participants last post by  oldtimer  
#1 ·
Just got a job to wire a dental office in an old building that has been gutted and ready to wire. Any special things on grounding. There will be no backup gen so I think I need emergency lights in all the patient rooms etc. and the x-ray has low volt controls. Will be be putting all most all equipment on dedicated circuits. I need 60 circuits and no 240 circuits. Air, water heater etc are staying on old pannels so I am adding a new feeder and pannel for offices only.
 
#3 ·
Yeah, keep the article 517 requirements in mind for the exam rooms... that means a lot of HCFC cable. Other than that, it's pretty straightforward... just a regular office.

Check wall finish thicknesses! Depending on the type of x-ray equipment they are using, sometimes they'll do a double layer of 5/8 drywall to get the "lead equivalent" they need.
 
#6 ·
keep in mind the listing of the equipment.
I've been coming across alot of dental chairs , panaramic xrays, and air compressors that are not listed. The dentists are buying the stuff straight from china as it costs less, that is until they are required to get it all listed/certified.

Keep in mind that if the light switches for the patient care areas are in the patient care area, the circuit must be wired with HCFC.

Another issue I've been finding is that the dentists want to hang flat screen tvs for the patient to watch. The issue is the low voltage guys almost always run non plenum rated cables through the plenum ceilings, for the tvs.
 
#8 ·
Another issue I've been finding is that the dentists want to hang flat screen tvs for the patient to watch. The issue is the low voltage guys almost always run non plenum rated cables through the plenum ceilings, for the tvs.
I have worked in a ton of medical offices. Some done legally, some not. The only time I have ever seen a plenum ceiling was in a hospital, never a medical office. And I remember it vividly. OB/GYN. Was up in the lid and able to see into rooms through the returns, and it was not as nice as I thought it would be.
 
#7 ·
For a while we did nothing but dental offices. Miles and Miles of Hospital Grade Cable. In my opinion they were "over circuited". Dedicated runs for everything. I can remember pulling several home runs to one chair when a single 20 amp circuit would have sufficed.
 
#11 ·
I got thru the rough in ok. Just have to add some more exit lights. All I had to have was one 20 A feed to the chair and the "chair people" will handle the disconnect ( recepticle and all the chair equipment plugs in) Also I have to get documintation on the x ray machine. Those people said verbally that the contractor only needed one layer of 5/8 drywall for the radiation and inspector needs that in writing. I didn't have the window sinage recepticles in yet but insp never caught that one.:whistling2: No anistesia ( need spelling police ) is used here so that helped. Ran lots of low voltage wire but don't have to do anything else with that