Sorry for my misunderstanding
unfortunately, you have some misconceptions about how an electrical panel is rated. I suggest you read the code book or take some courses. Your statement is 90% wrong.Why are people putting 3/0 cu on a 200 amp single phase 3 wire service. They keep quoting 310.15 using 90 degree rating for copper as being 200 amp. I am questioning if they even understand what happens inside an electrical panel.
Let me explain. Each ungrounded conductor of the service carries 100 amp a piece of the 200 amp rated service. Meaning....... each conductor does not have to be rated at 200 amps. This is why table 310.15(b)(6) exists, to keep "people" from trying to tell you to do something you don't need to.
Sorry. This is just driving me crazy.
Wow!Why are people putting 3/0 cu on a 200 amp single phase 3 wire service. They keep quoting 310.15 using 90 degree rating for copper as being 200 amp. I am questioning if they even understand what happens inside an electrical panel.
Let me explain. Each ungrounded conductor of the service carries 100 amp a piece of the 200 amp rated service. Meaning....... each conductor does not have to be rated at 200 amps. This is why table 310.15(b)(6) exists, to keep "people" from trying to tell you to do something you don't need to.
Sorry. This is just driving me crazy.
Start here:Let me explain. Each ungrounded conductor of the service carries 100 amp a piece of the 200 amp rated service. Meaning....... each conductor does not have to be rated at 200 amps.
Really?Perhaps they use 3/0 because they have enough on hand to do the job, as opposed to spending time & money buying more 2/0.
Jez sayin.
Perhaps they use 3/0 because because 2/0 is only good for 175 amps
As long as he isn't posting on DIY chatroom he is ok :laughing:I just had this conversation/argument with my father-in-law. He was positive that a 200A service only had 100A on each leg. He is retired GTE. He should stick to telco.
He also said that all the breakers on one side of the panel was one leg, and the other was on the other side of the panel.:blink:
Stubborn, he is.