I'm installing a car charger circuit. The specs for the car charger say 50A breaker, 40A operating current and 6AWG wire. The Tesla Car Charger spec is attached. This is a 25' run.
2014 NEC table 310.15(B)(16) says 8 AWG THHN 90C will support 55A
The Southwire I buy at Home Depot is THHN 90C.
Note that 125% of 40A operating current is 50A which can be met by 8 AWG THHN 90C wire.
I've also seen this "discrepancy" in DYI and other electrical forums.
Am I missing something? Why do I keep seeing 6 AWG required for 40A circuits?
It also looks like there may be an inrush issue here because of the 50A breaker required for an operating current of 40A. Maybe this is adding to my confusion.
Anyway, I estimated for 6AWG but would rather pull 8AWG through the 3/4" conduit.
2014 NEC table 310.15(B)(16) says 8 AWG THHN 90C will support 55A
The Southwire I buy at Home Depot is THHN 90C.
Note that 125% of 40A operating current is 50A which can be met by 8 AWG THHN 90C wire.
I've also seen this "discrepancy" in DYI and other electrical forums.
Am I missing something? Why do I keep seeing 6 AWG required for 40A circuits?
It also looks like there may be an inrush issue here because of the 50A breaker required for an operating current of 40A. Maybe this is adding to my confusion.
Anyway, I estimated for 6AWG but would rather pull 8AWG through the 3/4" conduit.