Any foreseeable code issue feeding a sub panel with 6/3 and a 70 amp breaker?
Typical residential sub panel is fed with #6 and a 60, but I found myself thinking the other day "why couldn't I slap a 70 in there"?
 
#5 ·
That's a good point. Yes, we have a similar rule, and yes it would allow 70A. However, that just seems like the kind of thing that an inspector would nail you for. I'd definitely ask first.

Our underground-rated #6 is rated 60C (max 55A), but the rest of it that you normally see is all rated 90C. 75C and 90C have the same ampacity (65A) so that isn't an issue.
 
#4 ·

Table 310.15(B)(16) (formerly Table 310.16) Allowable Ampacities of Insulated Conductors Rated Up to and Including 2000
Volts, 60°C Through 90°C (140°F Through 194°F), Not More Than Three Current-Carrying Conductors in Raceway, Cable, or
Earth (Directly Buried), Based on Ambient Temperature of 30°C (86°F)*
 
#13 ·
read nec sec. 215.2 (A) (1), last sentence. The minimum feeder-cuircuit conductor size, before the application of any adjustment or correction factors, shall have an allowable ampacity not less then the noncontinuous load plus 125 percent of the continuous load. so if you were completely loading the 70 amp subpanel with a continuos load, 70 times 1.25= 87.5 amps, or even half the load being continuous at 78.5 amps, you would still be over. One can't just use t310.16.
0
 
#18 ·
We should always go by the code but the bottom line is that there is a good safety factor in what the code wishes. I do not deviate but some times people wonder what will a conductor take. A #12 cu in free air will conduct 200 amps before starting to melt. The insulation is what we are protecting and therefore the premises.
 
#19 ·
We should always go by the code but the bottom line is that there is a good safety factor in what the code wishes. I do not deviate but some times people wonder what will a conductor take. A #12 cu in free air will conduct 200 amps before starting to melt. The insulation is what we are protecting and therefore the premises.
I'll say Amen to that brother.