Okay, so somehow I have never noticed this line in the book before, and no inspector has ever called me on it. Maybe I am misunderstanding it.
What it seems to be saying to me is that you can only load single conductors in free air up to 85% of their amperage, even when they are properly installed and spaced.
So where I have a 400A splitter served by 3 x ACWU 1-C 350kcmil the book says that is good for 445A at 90C. That's what I normally use. It's rated for 395A at 75C so I would think that there is even some leeway, there. This rule, 8-104(5)b seems to say, though, that a 100% continuous duty breaker switch rated at 400A "shall not exceed 85% of the allowable ampacties of single conductors selected in accordance with section 4"
That would seem to indicate that the actual maximum amperage of my AWCU 350kcmil is 445 x 0.85 = 378A.
Am I reading this right? Is this NEW? Is all of my cable under-sized?
What it seems to be saying to me is that you can only load single conductors in free air up to 85% of their amperage, even when they are properly installed and spaced.
So where I have a 400A splitter served by 3 x ACWU 1-C 350kcmil the book says that is good for 445A at 90C. That's what I normally use. It's rated for 395A at 75C so I would think that there is even some leeway, there. This rule, 8-104(5)b seems to say, though, that a 100% continuous duty breaker switch rated at 400A "shall not exceed 85% of the allowable ampacties of single conductors selected in accordance with section 4"