I'm in an argument with the refrigeration guy and he's being a stubborn jackass, so please vindicate me.
Ice-making machine. Nameplate: 208 - 230 VAC single-phase, Max OCPD: 40 amps, minimum circuit ampacity: 23.8 amps.
Installing a 40 amp breaker, what is the ABSOLUTE MINIMUM size conductor you can legally run for this circuit? The wiring method is MC cable, installed in a drop ceiling with ambient temperatures below 86 fahrenheit.
My vote is that #12 MC cable could be installed at the absolute minimum (not preferred, but NEC compliant).
Ice-making machine. Nameplate: 208 - 230 VAC single-phase, Max OCPD: 40 amps, minimum circuit ampacity: 23.8 amps.
Installing a 40 amp breaker, what is the ABSOLUTE MINIMUM size conductor you can legally run for this circuit? The wiring method is MC cable, installed in a drop ceiling with ambient temperatures below 86 fahrenheit.
My vote is that #12 MC cable could be installed at the absolute minimum (not preferred, but NEC compliant).