Circuit Loading for Baseboard Heaters

CEC
11K views 9 replies 5 participants last post by  ChicoQuente  
#1 ·
Trying to iron out something in my head over branch circuit loads, I am a bit rusty so please take it easy on me

62-114(6) basically says if your breaker is marked for continuous operation at 100% you can load it to 100%

So by that logic on a 20 amp breaker you can load 4800W of heat. If it's marked for 80% you can load 3840W assuming 240V heaters

So if you are asked in theory "How much wattage of baseboard heat can you put on a branch circuit at 208V" - Do you use 80% of 100%?

This seems super elementary but I've honestly forgotten how to do loading on branch circuits for baseboard heaters.. yikes
 
#4 ·
There are no breakers rated for 100% available under 250 amps currently.
Rumours of the new Leviton ones being rated at 100% but I’ve yet to see any proof of that.

Keep in mind that for fixed resistive heat the conductors can be loaded to 100%. 62-114(7)

As Eddy said, you can have the conductors at 100%. You are allowed to upsize the breaker to account for the higher current. ie, 20A breaker on #14 cable.
By that logic I still don't understand why people are saying you can only load 3840W on a 20A circuit for 240V heaters. I guess 62-114(6) overrules (7)

Like in what situation could I load 4400W vs 3840W if the rule says I can load it at 100%?

Think I am overthinking this, feeling dumb
 
#3 ·
So if you are asked in theory "How much wattage of baseboard heat can you put on a branch circuit at 208V" - Do you use 80% of 100%?
As Eddy said, you can have the conductors at 100%. You are allowed to upsize the breaker to account for the higher current. ie, 20A breaker on #14 cable.
 
#10 ·
Sorry to revive an old thread but this one is relevant to my question. I am looking to add the following heater to a mud room we have as we don't really have the space to accomodate a traditional baseboard.

Would a Braun Wall Heater (ASIN: B0002YTLBI) still be considered a fixed resistive load for load calculation or would the blower in it negate that?

I currently have a circuit that is 240V/15A with a 500W, and 1500W baseboard on it. If I can bump the breaker to 20A to accommodate the heater above (1000W) it would save me a ton of work in running the wire for it.

As a new user I can not include a link unfortunately directly to the unit I am considering.