I've spent way too many hours studying derating, only to find that anything & everything I thought I'd learned has turned out to not be necessarily true. Can y'all correct me on what I think I now know?
Ambient temperature aside (since I haven't studied it yet) with respect to bundling and not in a raceway, this is how we derate NM cable:
Ambient temperature aside (since I haven't studied it yet) with respect to bundling and not in a raceway, this is how we derate NM cable:
- We use the 90°C column in Table 310.16 (because 334.80 says so). Is this because all NM is THHN or just because code says so?
- We derate from that column, but we can't go any lower in ampacity than what's in the 60°C column (because 334.80 says so).
- And for gauges that are 10 AWG to 18 AWG, we use the 60°C column and 240.4(D) which states 18 AWG 7 amps, 16 AWG is 10 amps. For some reason those two aren't listed in the 60°C column in Table 310.16.
- If we happen to have just one NM cable with at least 4 current-carrying conductors, we derate it, because Table 310.15(C)(1) says so. "*Number of conductors is the total number of conductors IN the raceway or cable, including spare conductors." I've never seen 12/4 NM, but I figure it probably exists.
- When we bundle and not space NM cables (for lengths greater than 24") we then derate.
- If we have three 12/3 conductors (not in a raceway) that are bundled, is that considered a count of
sixnine current carrying-conductors? Since we count each current-carrying conductor in a single NM cable. - If we have a single 12/3 Romex, that's not going to be derated, is the ampacity we expect to use in the 90°C column of Table 310.16 (which is 30 amps) or is it the 60°C column which is 20 amps? I've always worked with 12 AWG was 20 amps, so now I question everything I ever thought I knew.
- When we're derating other insulated conductors, is Table 310.16 pretty straight forward, like THWN is 75°C column, or is it as convoluted as derating NM cable?