I made an observation while the electric oven was sitting on the floor. The service from the house is 220vac 50amp using 6-3 aluminum wire.
The GE oven connects to the circuit using 14-3 copper

What am I missing here? Wouldn’t the 14-3 melt down and catch fire long before, or if ever, the break would trip?
 
#10 ·
The 30" oven I installed at my house 2 years ago is rated 3.6KW @ 120/240. That works out to 15 amps.

Is the #14 protected by a 15 amp breaker?
The 14 gauge wire is coming from the oven and terminating in the splice box from the house. The feed from the house is a 50amp service, protected by a 50 2 pole breaker feed over a 6-3 aluminum conductor.
 
#4 ·
when you say the service from the house is 50A
do you mean the circuit leaving the breaker panel and a 50A breaker?

when you say an electric oven
do you mean just an oven, or a complete range with top burners also?

if you are talking about the cord from the oven to the receptacle?
or a hard wired whip?
the mfg built that to handle the load, possibly higher temperature insulation

if you are talking about the wire inside the oven ?
that insulation is a higher temp than 90*C
which makes the ampacity higher than the 90*C rating which is 25A

the reason we put #14 on a 15A breaker has to do with the temperature ratings of the breaker and the terminations
very different animal than inside the oven or range where everything is always hot when in use
 
#17 ·
Chassis wiring is different, and they follow their own set of rules.
Same as Power Company supplying 200A O/H service on #2 AL. If you look up on Priory Wire, it's rated as high as 180A. It's in free air thou.

See attached, note the max amps for wires used as 'chassis' wiring.

#16 is good for 22A.

Image
 
#21 ·
Saying 14 gauge without specifying the type of wire is not saying much. One of the types of wire used in cooking and heating equipment is SRML it’s also used for motor leads. A 14 gauge in this type is rated at 40 amps.

You would need to consider the wattage of the heating elements and the temperature of the environment that the wire operates in as well as the duty cycle of the appliance. Connection terminations types are just as important. I’m sure that the manufacturer covered the testing and rating of the internal materials on their end. The question then becomes did you follow their guidelines for the connections on your end. Standard splicing materials may not be rated for the temperature or dissimilar metals. Following the instructions is important to prevent failures.
 
#22 ·
Again,

I did not install it. I only worked on the cabinet, hence why I am asking the question because I don’t even know what I don’t know.

An electrician installed the oven. When the oven was sitting out I made the observation that the wires on the oven we considerably smaller then the wires hanging out of the wall. Also the wires on the oven were copper and the wall was aluminum.

I don’t know if this was right or wrong. I work on cabinetry.