Floor outlets

1 reading
3.9K views 16 replies 6 participants last post by  samgregger  
#1 ·
I came across a couple floor outlets without a receptacle in them. The church wants to put them back into service. Their very small, 2.5" sleeves. Screw holes for the outlets are 2 3/8 center to center. Anyone ever dealt with flour outlets this small? Looking for a mfg that would have them, our supply houses are stumped.
Josh
Michigan

Sent from my SM-G920P using Tapatalk
 
#4 ·
Agreed on the egc but there's a chance we can pull new wire in, I've done it in worse looking boxes and pipe. I've debated cutting a new floor box in, the only issue is the pipe is only about 2-2.5" below the floor. Not a major problem though, just a PIA!!
Thx
Josh

Sent from my SM-G920P using Tapatalk
 
#13 ·
Walkerduct (Wiremold// Legrand) trimmings?

Your picture shows what appears to be 2.5" presets... or the grandfather thereof.

436- 2-2 3/8 2 3/8" [64mm] high

This is the Walkerduct number for the pre-set in your photograph -- though yours looks considerably older, and is the basis for # 436-2-2 3/8.

You want an "ACTIVATION PACKAGE" for for this preset.

"A wide range of service fittings are available to meet all applications:
See noted literature for detailed information.


â–  Flush brass, aluminum and polycarbonate fittings (ED850).
â–  Flush carpet activation plates (ED850).
â–  525 Series pedestal fittings (ED1225)."

Go to Wiremold.com