high leg service

2.5K views 11 replies 7 participants last post by  varmit  
#1 ·
I'm working for a client that has a high leg service. There has been a lot of strange occurrences in the building electrical. They have taken and shared a neutral on all of the a and c phases. This doesn't seem proper to me. Can anyone lend any knowledge on this
 
#4 ·
My local utility rarely uses high leg services any more. They use to be somewhat common for small commercial businesses that had a very limited 3 phase load.
Neutrals were shared sometimes. Unlike single phase services where the phases are 180 degrees out of phase with each other , in 3 phase they are out of phase by 120 degrees, and when sharing neuts the current isn't fully cancelled out when using two phases.
 
#7 · (Edited)
So, if you put a 120v load on B leg the factory sealed smoke would escape. Look for a drawing of a high leg delta. You should understand then.:) On a high leg delta "B" phase is 208volts to ground.
 
#11 ·
Draw out the transformer connections...you will see that A and C are connected to a single transformer winding that has a center tap. This part of the 4 wire delta system is exactly the same as a standard 120/240 volt system and there is no problem of sharing the neutral other than the common means of disconnect (breaker handle tie) required by 210.4(B).