I work at an industrial facility with a lot of old equipment. I was always taught to meggar a motor to find out if it is bad. Is it best to meg between windings or meg to ground . thank you for your time
Unless its a 500HP DC motor in a bad spot at 3:30 on a Friday afternoon!" I love the smell of a burned-out motor in the morning"
:laughing::laughing:
megging is a good way but follow the first rule with motors" I love the smell of a burned-out motor in the morning"
:laughing::laughing:
That's how a ohmmeter measures resistance... A small dc voltage, calculates resistance based on current.John Valdes said:I once had an idea I never put to use or tried out. What if you used a small DC power supply connected to the individual coils with your meter in series and reading amps. Would this not be a way to check winding health? You could even use an AC supply and measure that current. I'm talking very low voltage like in the range of 0-24 ac or dc volts.
But we would concern ourselves only with the current making sure we had the exact same voltage applied to each coil. With a meter in series we can measure very low current. Milliamps and compare readings.
That's been my experience. Some people here disagree with that though.I hate to say it but if it doesn't measure a short to ground or open circuit with a regular meter, the chances a megger will find anything conclusive are slim. In my mind an impulse tester like a baker tester or sweep frequency analyzer is really the only thing that can conclusively tell you a motor is healthy. These sorts of tests are probably not worth doing on motors less than 50 or 100hp though.
But an ohm meter cannot read resistance on a bigger motor because the windings resistance is to low.That's how a ohmmeter measures resistance... A small dc voltage, calculates resistance based on current.
An Lcr meter measures impedance with an ac voltage more or less the same way.
Baker surge testers at one time were used exclusively by motor shops. It is how they determine motor winding health.I hate to say it but if it doesn't measure a short to ground or open circuit with a regular meter, the chances a megger will find anything conclusive are slim. In my mind an impulse tester like a baker tester or sweep frequency analyzer is really the only thing that can conclusively tell you a motor is healthy. These sorts of tests are probably not worth doing on motors less than 50 or 100hp though.
And has weep holes that allow water to drain from the motor. We loved those facilities as a motor shop.In this age where damn near everything installed new is on a VFD, the VFD is a fine troubleshooting tool in itself. If it says current limit, overload, ground fault, etc.... believe it. Pretty good chance (if it's not mechanically bound) it's the motor or the wire between the drive and the motor. Can't tell you how many "bad drives" I know people have replaced for these "faults", when the fault was actually diagnosing the motor. Nothing wrong with the drive.
While the tests can get exotic if you like, the old sniff test in the peckerhead will sort out the lion's share of suspect bad motors. No need to make it harder than it needs to be.
I've done a lot of work in food and pharma factories, where hundreds and hundreds of washdown rated motors are subjected to daily chemical and hot water washdown. EVERY motor and every local disconnect in such plants will meg "bad". By the way, "washdown rated" and "IP67" are pure marketing terms that means that it takes a little bit longer for water to get inside. :laughing:
Supro 500 baby....I work at an industrial facility with a lot of old equipment. I was always taught to meggar a motor to find out if it is bad. Is it best to meg between windings or meg to ground . thank you for your time
Omfg, you people own stock in that company or something?Supro 500 baby....
Be careful that this is not taken out of context! :whistling2:... the old sniff test in the peckerhead ...
Be careful that this is not taken out of context! :whistling2:
I think I posted this some time ago, but I have it on my "permanent record" with HR that I had been using "inappropriate terminology" when doing training classes on VFDs, because I called the motor termination box a "peckerhead". I was asked to provide proof in writing that the term came from some meaning other than what it appears to come from, and I could not find anything about the origin. HR on the other hand found something in writing that claimed it IS what it sounds like, and ordered me to change all of my presentations that used that term. I missed one and got written up after someone else used it.