interesting question: will the multimeter blow?

5.4K views 25 replies 19 participants last post by  oliquir  
#1 ·
I know this question will get some guys

one guy have a multimeter, and this meter is rating for 1000V, 200amps, this guy use this meter to test a fuse in a live switch gear(by the way, the fuse is blow in this case), the voltage of the load is 600V, the load is now 400amps

1. situation A: he set the meter at the voltage testing setting, and test both side of the fuse, will the multimeter blow?

2. situation B: he set the meter at the current testing setting, and test both side of the fuse, will the multimeter blow?
 
#2 ·
If the meter is made in such a way that it will try and carry the load the internal fuse will blow unless it's a UEI meter and it will just explode in your hand (had that happen at 480v).

Testing each side of a blown fuse to ground will give you voltage but doesn't really tell you anything about the fuse.
 
  • Like
Reactions: Jmcstevenson
#3 ·
Question back for you

What multi meter is good for 200 amps???????
Voltage check will not blow a meter unless you go over voltage rating of meter.
Back in the days of Simpson meters, before digital meters I modified a meter to put in a reversing switch for the DC. Only problem was it was a 125vdc switch and when testing 250v dc the meter went BOOM. Actually blew the meter case in half but contained the explosion. I'll never forget the look on mt apprentices face, "priceless" when the building shut down.
 
#4 ·
What multi meter is good for 200 amps???????
Voltage check will not blow a meter unless you go over voltage rating of meter.
Back in the days of Simpson meters, before digital meters I modified a meter to put in a reversing switch for the DC. Only problem was it was a 125vdc switch and when testing 250v dc the meter went BOOM. Actually blew the meter case in half but contained the explosion. I'll never forget the look on mt apprentices face, "priceless" when the building shut down.
"when the building shutdown" :laughing:
 
#10 ·
Is the meter a clamp-on? I don't know of any basic multimeters that can handle 200 amps though a lot of them will do 20 amps.

Assuming the meter is used correctly, measuring voltage across a fuse (blown or not) will not harm the meter.

Measuring current across a blown fuse (direct reading, not clamp-on) will cause the meter to read the current that would be going through the fuse if it were not blown.

If the meter is set to read 20 amps and the load across the blown fuse is 6 amps, then the meter will read 6 amps. If the load is 200 amps.....BOOM!!!

I also know for a fact that using a basic multimeter to read voltage on a 2300 volt transformer will send a guy to the burn ward.........wasn't there but had to repair the aftermath.

Note; a lot of more modern meters have fuses inside the case and the fuse will blow, not the meter. Some meters have fuses on everything but the 10 or 20 amp jacks.
 
#11 ·
I know this question will get some guys

one guy have a multimeter, and this meter is rating for 1000V, 200amps, this guy use this meter to test a fuse in a live switch gear(by the way, the fuse is blow in this case), the voltage of the load is 600V, the load is now 400amps

1. situation A: he set the meter at the voltage testing setting, and test both side of the fuse, will the multimeter blow?

2. situation B: he set the meter at the current testing setting, and test both side of the fuse, will the multimeter blow?

the answer:
1. no
2. yes

I guess some people don't know how a multimeter works:
when checking the voltage, the meter is in parallel
and when checking the current, the meter is in series
 
#15 ·
Where do you find these questions mike? I'm guessing you're picking
through questions from trade school tests/practice sheets.
P&L
 
  • Like
Reactions: mike883
#12 ·
#16 · (Edited)
the answer:
1. no
2. yes

I guess some people don't know how a multimeter works:
when checking the voltage, the meter is in parallel
and when checking the current, the meter is in series
.
F**k you're stupid!

First off, you don't use a multimeter to test current when you are dealing with anything over 20 amps, and then, usually you are dealing with milli-amps, and usually with DC/ And if you parallel your leads from one end of the fuse to the other, your meter would explode
You use an Amprobe or other such clamp type meter.

you will blow the 200 ua fuse when you test current to ground , which in this case you would have voltage at the line side of the fuse.
BUT, since you stated the fuse was blown, there is no voltage on the load side, so you wouldn't blow the meter.

Checking to see if you have voltage at both ends of the fuse usually indicates the fuse is good ( yes you can get feedback, but thats a different post foryou to invent)

Just exactly what is you level of apprenticeship or are you even in the trade?
The reason I ask, is that most of your questions seem to be what a 1st year or pre-employment would ask. Just enough knowledge to think you know a lot