Anyone know where the rule is for this? I'm reading through trying to find it...
#2 ·
300.14 Length of Free Conductors at Outlets, Junctions, and Switch Points. At least 150 mm (6 in.) of free conductor, measured from the point in the box where it emerges from its raceway or cable sheath, shall be left at each outlet, junction, and switch point for splices or the connection of luminaires or devices. Where the opening to an outlet, junction, or switch point is less than 200 mm (8 in.) in any dimension, each conductor shall be long enough to extend at least 75 mm (3 in.) outside the opening.
Exception:  Conductors that are not spliced or terminated at the outlet, junction, or switch point shall not be required to comply with 300.14.
#3 ·
HARRY304E said:
300.14 Length of Free Conductors at Outlets, Junctions, and Switch Points. At least 150 mm (6 in.) of free conductor, measured from the point in the box where it emerges from its raceway or cable sheath, shall be left at each outlet, junction, and switch point for splices or the connection of luminaires or devices. Where the opening to an outlet, junction, or switch point is less than 200 mm (8 in.) in any dimension, each conductor shall be long enough to extend at least 75 mm (3 in.) outside the opening. Exception:  Conductors that are not spliced or terminated at the outlet, junction, or switch point shall not be required to comply with 300.14.
canada harry
#6 · (Edited)
12-3000 Outlet boxes
(6) At least 150 mm of free conductor shall be left at each outlet for making of joints or the connection of
electrical equipment, unless the conductors are intended to loop through lampholders, receptacles, or
similar devices without joints.
I wish there was a rule for the max amount of wire in a box. 24inches stuffed into the box is the number one reason for drywaller-nicked wires and half my coworkers refuse to believe it. :wallbash:
#7 ·
I think being near the bottom of the food chain contributes to more nicked wire. You have a pep talk with them and inform them you charge the GC for repairs, follow through, and you only have to do it one time.