I have a air handler that I need to run wires to. On the nameplate it says MCA of 29.25 amps and MOP 50 amps. My understanding from what I read online I size my wire based on the MCA. So I can have #10 wire ran to it and landed on a 50 amp breaker is that correct? My boss said that’s not correct and I need to always size my wire based on the max Overcurrent rating. There’s nothing wrong with that except for the added costs so I’m just doing what he says since he’s the boss. However I would really like to have any other opinions on if I was doing it the correct way or if his way was correct. Thank you!