OCP on Water Heater
2 reading
10K views 31 replies 9 participants last post by  waco
#1 ·
What size OCP are the rest of you putting on a water heater in a dewelling that has a total connected load of 3500w or 3380w @ 208?
#4 ·
Water Heater OCP
Maybe, and I probably would, put in the 25, but I feel an inspector must go by the wording in the code. 25.24 is above 25 and the code allows me to go up to the next standard, I know its splitting hairs but that is what the code says. If I don't have a 25, I'll put in the 30.
220.5 (B) allows the installer to drop a fraction of an amp but does not require it.
#24 ·
I believe the OP is referring to a standard 4500 watt water heater.
At 240 volts, 4500 watts = 18.75 amps. X 1.25=23.4 amps. In this case, I use #10's and a 25 amp breaker.
The same unit operated at 208 volts will consume 3380 watts, and draw 16.25 amps. 16.25 X 1.25 = 20.3. According to 220.5 (B), you're allowed to drop the fraction if it's less than 0.5 In this case I use a 20 amp breaker and #12's.
I was called on this once by a highly respected inspector, and had to provide code references, but I think he already knew the answer, and was just testing me.
Around here, no disconnect is required for anything except an outdoor HVAC unit on residential. On commercial/industrial, you'll need a disconnect if you can't see the panel from the water heater. I usually use the 30 amp pull-out A/C disconnects.
Rob
#26 · (Edited)
Micro, I don’t see a problem with how you’re doing it, especially since in this case that .3A is virtually nothing, but as usual, the code seems less than homogenous about this.
Some other less congenial inspector may call you on it again someday, as it could be argued that 422 replaces 220 for appliance branch circuits and the text of 220.5 that allows the dropping of less than .5A for branch circuit and feeder sizing is not mentioned for sizing appliance branch circuits in 422.10.
Also, since according to 422.11[e], the OCP is sized from the rating of the appliance, not the branch circuit, again that .3A would have to remain for minimum sizing of the OCP.
Since you would probably want to go to the next standard size up as allowed by 240.4, you would most likely end up with #10 and 25A OCP for the 208V water heater.
Anyway, keep your sword at the ready just in case.