What size OCP are the rest of you putting on a water heater in a dewelling that has a total connected load of 3500w or 3380w @ 208?
3500 watt water heater 30 amps.
3500/208x1.5=25.24 amps next size up 30 amps
3380 watt water heater 25 amps.
3380/208x1.5=24.38 amps next size up 25 amps.
422.11 (E) (3)
I agree 100%3500/208 = 16.8269......
16.8269 * 1.5 = 25.24.
Drop the .24 because it's less than .5 and I'd slap a 25A DP breaker in that beeotch.
Just by example if it were 25.6 then a 30A is an option, but a 25A would be ok too.
Micro, I don’t see a problem with how you’re doing it, especially since in this case that .3A is virtually nothing, but as usual, the code seems less than homogenous about this.I believe the OP is referring to a standard 4500 watt water heater.
The same unit operated at 208 volts will consume 3380 watts, and draw 16.25 amps. 16.25 X 1.25 = 20.3. According to 220.5 (B), you're allowed to drop the fraction if it's less than 0.5 In this case I use a 20 amp breaker and #12's.
I was called on this once by a highly respected inspector, and had to provide code references, but I think he already knew the answer, and was just testing me.