Weird call today.
I was called to a water pumphouse the other day to connect a large trailer mounted 600v 400a backup generator because the genset inside the plant dropped a valve and has to go for service.
The genset came with four cables. Three hots and a ground. I noticed on the nameplate for the temporary genset that the generator windings are connected in Wye configuration, but I didn't have a neutral cable supplied and there was a bonding jumper inside the connection panel on the genset, so I just connected the genset grounding cable to the ground bus inside the plant MCC, the hots to the emergency lugs in the xfer switch and let her buck. I checked rotation first, so things fired up without a problem. VFDs are happy, all other loads in the plant chooch along fine.
The trouble came today when I was called back because the pumps wouldn't run in auto. I jacked into the PLC and found that the phase loss monitor status was in series with all pump permissions.
Its the oddest thing. With equal voltage and phase rotation on both utility power and the backup generator power the phase loss monitor would drop into alarm on transfer to backup power. I replaced the unit with a new Carlo Gavazzi phase loss monitor and its the same thing! If I change the phase sequence going in to the phase loss monitor it will come out of alarm and show OK. The same thing happens on utility power if I change the phase sequence going into the monitor, it will go into alarm on BAC and show fine on CAB.
Long and short of it, the PLM seems to want a certain sequence, but even when that sequence is the same according to my meter (and the ATL motors) it still doesn't like the difference between utility and backup power. This wasn't an issue with the pad mounted generator in the plant.
I think its because the main service is Delta and the generator power is Wye, but I'm not experienced enough with how the two different systems behave to know for sure.
How in the hell could this be happening?
I was called to a water pumphouse the other day to connect a large trailer mounted 600v 400a backup generator because the genset inside the plant dropped a valve and has to go for service.
The genset came with four cables. Three hots and a ground. I noticed on the nameplate for the temporary genset that the generator windings are connected in Wye configuration, but I didn't have a neutral cable supplied and there was a bonding jumper inside the connection panel on the genset, so I just connected the genset grounding cable to the ground bus inside the plant MCC, the hots to the emergency lugs in the xfer switch and let her buck. I checked rotation first, so things fired up without a problem. VFDs are happy, all other loads in the plant chooch along fine.
The trouble came today when I was called back because the pumps wouldn't run in auto. I jacked into the PLC and found that the phase loss monitor status was in series with all pump permissions.
Its the oddest thing. With equal voltage and phase rotation on both utility power and the backup generator power the phase loss monitor would drop into alarm on transfer to backup power. I replaced the unit with a new Carlo Gavazzi phase loss monitor and its the same thing! If I change the phase sequence going in to the phase loss monitor it will come out of alarm and show OK. The same thing happens on utility power if I change the phase sequence going into the monitor, it will go into alarm on BAC and show fine on CAB.
Long and short of it, the PLM seems to want a certain sequence, but even when that sequence is the same according to my meter (and the ATL motors) it still doesn't like the difference between utility and backup power. This wasn't an issue with the pad mounted generator in the plant.
I think its because the main service is Delta and the generator power is Wye, but I'm not experienced enough with how the two different systems behave to know for sure.
How in the hell could this be happening?