Weird call today.


I was called to a water pumphouse the other day to connect a large trailer mounted 600v 400a backup generator because the genset inside the plant dropped a valve and has to go for service.


The genset came with four cables. Three hots and a ground. I noticed on the nameplate for the temporary genset that the generator windings are connected in Wye configuration, but I didn't have a neutral cable supplied and there was a bonding jumper inside the connection panel on the genset, so I just connected the genset grounding cable to the ground bus inside the plant MCC, the hots to the emergency lugs in the xfer switch and let her buck. I checked rotation first, so things fired up without a problem. VFDs are happy, all other loads in the plant chooch along fine.


The trouble came today when I was called back because the pumps wouldn't run in auto. I jacked into the PLC and found that the phase loss monitor status was in series with all pump permissions.


Its the oddest thing. With equal voltage and phase rotation on both utility power and the backup generator power the phase loss monitor would drop into alarm on transfer to backup power. I replaced the unit with a new Carlo Gavazzi phase loss monitor and its the same thing! If I change the phase sequence going in to the phase loss monitor it will come out of alarm and show OK. The same thing happens on utility power if I change the phase sequence going into the monitor, it will go into alarm on BAC and show fine on CAB.


Long and short of it, the PLM seems to want a certain sequence, but even when that sequence is the same according to my meter (and the ATL motors) it still doesn't like the difference between utility and backup power. This wasn't an issue with the pad mounted generator in the plant.


I think its because the main service is Delta and the generator power is Wye, but I'm not experienced enough with how the two different systems behave to know for sure.



How in the hell could this be happening?
 
#3 ·
The electronic phase monitors are more "picky" about true ABC sequence. ABC, BCA, or CAB connections are all the same to most electrical devices. (will result in same rotation) The phase monitor requires line 1 = A, line 2 = B and line 3 = C For the output to turn on. Unless you have a scope to use, you will need to do a trial and error connection of the phase monitor. VFDs do not care about the line side phase arraignment.
 
#5 ·
I agree. Having built one in the past, the issue comes down to how you measure it electronically. We can't measure a zero-cross point, because you can't measure zero effectively. So what you do is measure a point where the phases cross each other. This is called a Phase-Locked-Loop (PLL) detector circuit. But to save money, most of the low cost PMs will only use two PLLs, so to determine rotation sequence, you must pick a starting point, look for it, then time the others from that. So with that design, it MUST be A, followed by B, followed by C. Even though B-C-A and C-A-B are the same RELATIVE sequence, the problem is the time between the detection of the two phases and where it expects the time gap for the third one is off.

There are other phase detection designs that don't have that issue, but that's the cheapest way to do it so it's the most common.
 
#8 ·
Yes, a design using 3 PLLs would not know or care if it was ABC, CAB or BCA. It's just that the majority of cheaper units don't use 3. To make it work, you simply roll the conductors into it until it's satisfied. That was probably in the instructions, but who reads those...
 
#7 ·
I'm not buying any of the explanations.

We are basically ARBITRARILY designating one phase as "A" or "L1" or "U" or "T1" or "Brown" or "Red" or whatever you want to call it. Phase rotation only makes sense when we talk about the timing of the peaks or zero crossings relative to each other. And realistically the major reason for using a phasor display is strictly for figuring out whether or not all the CT's and PT's are wired correctly.

https://www.schneider-electric.cn/l...LOCAL/APS/205246_1676/Theory_and_instructions_on_how_to_use_the_phasor_tool.pdf

"A", "B", and "C" are ARBITRARY. As long as timing wise B lags A, C lags B, and A lags C, everything is identical. ABC = BCA = CAB. If it is the opposite where the phases LEAD each other than we have the opposite rotation and ACB = BAC = CBA. If I turn the display off, move ALL three leads by say one position so that for instance we have ABC to BCA and then use a power meter to check again, it looks IDENTICAL.

There is really only three ways that I can see a phase monitor not working correctly. The first one is that the phase rotation is reversed and nobody noticed until now. The second one is that the phase monitor has some screwy way that it is sensing one particular phase different from the others, such as if there are separate power inputs labeled say "L1" and "N" and that "A" input MUST be the same as "L1", or that the delta has a ground fault somewhere so that the control power input is "zero" so that instead of say 277/277/277 we have 480/480/0.
 
#10 ·
Weird call today.


I was called to a water pumphouse the other day to connect a large trailer mounted 600v 400a backup generator because the genset inside the plant dropped a valve and has to go for service.


The genset came with four cables. Three hots and a ground. I noticed on the nameplate for the temporary genset that the generator windings are connected in Wye configuration, but I didn't have a neutral cable supplied and there was a bonding jumper inside the connection panel on the genset, so I just connected the genset grounding cable to the ground bus inside the plant MCC, the hots to the emergency lugs in the xfer switch and let her buck. I checked rotation first, so things fired up without a problem. VFDs are happy, all other loads in the plant chooch along fine.


The trouble came today when I was called back because the pumps wouldn't run in auto. I jacked into the PLC and found that the phase loss monitor status was in series with all pump permissions.


Its the oddest thing. With equal voltage and phase rotation on both utility power and the backup generator power the phase loss monitor would drop into alarm on transfer to backup power. I replaced the unit with a new Carlo Gavazzi phase loss monitor and its the same thing! If I change the phase sequence going in to the phase loss monitor it will come out of alarm and show OK. The same thing happens on utility power if I change the phase sequence going into the monitor, it will go into alarm on BAC and show fine on CAB.


Long and short of it, the PLM seems to want a certain sequence, but even when that sequence is the same according to my meter (and the ATL motors) it still doesn't like the difference between utility and backup power. This wasn't an issue with the pad mounted generator in the plant.


I think its because the main service is Delta and the generator power is Wye, but I'm not experienced enough with how the two different systems behave to know for sure.



How in the hell could this be happening?

Hi, first post here for me...

same thing for me this week... today i instaled 2 new carlo gavazzi Phase Lost Monitor in 2 control panels,
Image


every thing work fine on utility power....

but it's an other story with the generator power.

in panel #1, PLM work fine,
in panel #2, PLM don't work, the output make on/off evry 2 secondes , i switch with the new one PLM in panel #1 and with this one, my output stay on. so i think 1 of my 2 new PLM are defect....
( Gavazzi says extremly rare defect on their products, and want it back to anlyse.. so they will not have my generator circuit to test it.. so they will say their product is not defect. )

but the old generator was delta , and the new generator is wye.... so it's maybe the source of my problem...

what's the solution???:
change carlo gavazzi for a siemens where i can adjuste up voltage / down voltage, and set a time delay reaction...? ( carlo have no adjustment)
harmonic problem ? expensif to fix..

thank you for your help.