PVC Male Adapter into a Service Panel Hub

1 reading
8.4K views 15 replies 9 participants last post by  99cents  
#1 ·
I don't exactly remember the problem, but I seem to recall that the PVC Male Adapters are not approved to screw into a metal Service Panel Hub because the Male Adapters are tapered and the hub is not. Am I remembering correctly??
 
#5 ·
The way I remember it, is that plumbing and electrical dies are the same. Tapered thread. But the female threads are different. Electrical is straight, plumbing is tapered.
The other difference is in PVC. Male adapters are straight. That’s why it won’t thread into a hub all the way. Two straight threads. And the hub is meant for tapered threads. It’s probably listed that way. There are many threads on here about it.
 
#7 · (Edited)
Maybe that would explain why MAs don't thread all the way into weatherproof boxes. So, if I took an MA & threaded it into a die to make its threads tapered, it should screw in all the way?
 
#6 ·
CEC
12-1112 Fittings

2) Female threaded PVC adapters shall be used together with a metal conduit nipple to terminate at threaded conduit entries in metal enclosures.
 
  • Like
Reactions: Kaitlyn
#15 · (Edited)
MH thread on the subject...

I like the close nipple & FA fix for the problem.
 
  • Like
Reactions: splatz